Hot Tapping on Natural Gas Line

03/01/2011 12:55 PM

I am working at Engro as project Engineer I need some information regarding rate of flow for natural gas line (Max and Min Limit) on which we have planned to perform hot tap. Is there any calculation to support this?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Hot Tapping on Natural Gas Line

03/01/2011 1:28 PM

Let me be the first, here, to congratulate you on your accomplishment of becoming a project Engineer.

What do you think the rate of flow is? I'd think it would be a number known to the project Engineer. Are there no flow meters anywhere?

But, since it isn't you should get with someone who knows the answer to the question as it relates to YOUR SPECIFIC pipeline. Maybe one of the old timers? He'd probably be able to explain what a hot tap is, too.

I'm sorry that I cannot help you, but I'm not qualified. I hope I have not been too harsh with you and hurt your feelings.

I've marked this OT.

Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#2

Re: Hot Tapping on Natural Gas Line

03/01/2011 1:58 PM

Are you aware of flow meters that can be strapped on the pipe to measure natural gas flow, and I think they are good enough to possibly be used for LACCT? In fact, if such a meter worked for you, you might not need to hot tap the line to install other devices (unless you are hot tapping for other reasons).

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3

Re: Hot Tapping on Natural Gas Line

03/01/2011 2:50 PM

Your title alone gets me very worried for your safety and the safety of others around you. Tapping into an active natural gas line should only be done by knowledgeable authorized. Your new job title shows that you can get the authority. CR4 though should not be your knowledge source. Your colleagues should be your knowledge source.

Be safe.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4
In reply to #3

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:03 PM

I don't have a dog in that fight first of all. I was merely pointing out they may not need to hot tap the line at all, and in many cases hot tapping a natural gas line is not only way dangerous, it could be illegal. Especially if safety constraints at the location such as nearby population or other industry could be harmed if something went wrong. If all he wants to know is gas flow, there are ways to deal with that without breaking into the line.

By the way, what new job title are you referring to redfred?

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#5
In reply to #4

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:14 PM

My reply was not a reply to you, James, it was a reply to "Guest". I was guessing that project Engineer at the company called Engro was the new title. Only a newbie would consider hot tapping into a natural gas line.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Anonymous Poster #1
#18
In reply to #5

Re: Hot Tapping on Natural Gas Line

03/02/2011 9:06 AM

...or someone wanting to steal natural gas!

Reply Off Topic (Score 5)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#6
In reply to #4

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:22 PM

Hi James Stewart,

redfred was not replying to you, but the OP (original poster). To reply to the OP, you click the Reply button In That Post. I replied to you specifically by clicking on the Reply button at the bottom of Your reply.

You can also see that replies to posts are indented from the left. Hope that clears things up a bit.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #6

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:47 PM

Thanks for pointing me in a better orientation.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:33 PM

Ignore this one

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:52 PM

Is this a steel high pressure main or a plastic distribution main?

If steel you're on your own as far as I'm concerned.

Plastic you will use hot weld, the fitting usually has a built in cutter which acts as an isolation valve when screwed back in.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#10

Re: Hot Tapping on Natural Gas Line

03/01/2011 3:54 PM

Maybe they've given you this project to see if you survive! (Or maybe they want to get rid of you.)

The "Darwin Awards" comes to mind when I hear of someone who doesn't know the flow rate in a pipe they are preparing to hot tap with no knowledge of the contents or the process.

A little bit like sending an apprentice to the shop to get a "long weight" (Or "long wait"). Your colleagues may be getting you to do some research and learn of the inherent dangers in what you are asking about.

__________________
Just an Engineer from the land down under.
Reply Off Topic (Score 5)
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#11

Re: Hot Tapping on Natural Gas Line

03/01/2011 6:34 PM

Hot taps on pipelines are not unusual; see this document with some stats from the US EPA

http://www.epa.gov/gasstar/documents/ll_hottaps.pdf

Pipelines carry gaseous or liquid money and are ALWAYS metered, usually at multiple points.

I can't possibly tell you what your company's flow rate for a particular segment of the pipeline is, but flow rate is a known at the metering points.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#12
In reply to #11

Re: Hot Tapping on Natural Gas Line

03/01/2011 9:27 PM

I didn't say that it wasn't done, I'm just worried about people coming to a public forum for help in doing a possibly dangerous operation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#13

Re: Hot Tapping on Natural Gas Line

03/01/2011 11:08 PM

The suggested product (gas) min. velocity during welding of a hottap shall be 1.3 fps (0.4 m/sec), and no limit on max. velocity.

..................................

__________________
It is better to be defeated on principles, than to win on lies!
Reply Score 1 for Good Answer
Participant

Join Date: Mar 2011
Posts: 3
#15
In reply to #13

Re: Hot Tapping on Natural Gas Line

03/02/2011 6:06 AM

MR. ABDEL HALIM: Can you please give the source or basis of these values. As they are not mentioned in API RP 2201. I need some authentic source. Regards, Bilal awan (OP)

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#16
In reply to #15

Re: Hot Tapping on Natural Gas Line

03/02/2011 7:09 AM

I'll second that request. Maybe I'm missing something, but I can't see what gas flowrate has to do with hot tapping.

Also in case there's any misunderstanding, I believe hot tapping is same as live tapping, ie tapping a working pipe. It doesn't (necessarily) mean thermal welding, though I believe that can be done. Natural gas in a pipe won't explode if the pipe is heated, as there is not a flammable mixture. Ethyne (acetylene) will explode per se, but that's another story.

Cheers.........Codey

__________________
Give masochists a fair crack of the whip
Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#19
In reply to #15

Re: Hot Tapping on Natural Gas Line

03/02/2011 11:14 PM

These data were extracted from a standard specification of an Egyptian oil exploring co. which stated that the reference is API 2201, but unfortunately I didn't found direct clear figures for min. and max velocities.

But at API 2201, I found at Para. 1.2 Referenced Publications the following standard: Battelle Institute "Investigation and Prediction of Cooling Rates During Pipeline Maintenance Welding and Battelle's Hottap Thermal Analysis Models", which is available from American Petroleum Institute.

__________________
It is better to be defeated on principles, than to win on lies!
Reply
Participant

Join Date: Mar 2011
Posts: 3
#20
In reply to #19

Re: Hot Tapping on Natural Gas Line

03/05/2011 4:18 PM

can you please help out to find the mentioned document. Battelle Institute "Investigation and Prediction of Cooling Rates During Pipeline Maintenance Welding and Battelle's Hottap Thermal Analysis Models", which is available from American Petroleum Institute.

Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#14

Re: Hot Tapping on Natural Gas Line

03/01/2011 11:49 PM

If the natural gas line is your company's or a customer's you should be able to find out from personnel who are responsible for it either what rate the natural gas is being put into it or being taken out of it. That should provide what rate it is going through it.

If the line isn't your company's or a customer's you probably should go through the proper channels before doing anything further. In the US of A simply asking what rate of flow there is in a pipe line that you have no reason to be interested in can possibly get you in big trouble with the DOT, Homeland Security, and all sorts of badges with acronyms like FBI, DEA, etc., on them.

Hot taps must be done by skilled, qualified and experienced personnel only! Is any life worth the risk if something should go wrong?

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Participant

Join Date: Oct 2012
Posts: 1
#21
In reply to #14

Re: Hot Tapping on Natural Gas Line

10/06/2012 8:44 PM

Dear all

I fully agree with old salt that "Hot taps must be done by skilled, qualified and experienced personnel only!"

The limitation required for wall thickness is to avoid overheating and burn-through. also there are some precautions and factors need to be considered in hot tapping

  1. base metal should be free of lamination at the area of welding hot tap fittings.
  2. hot tap fittings should be tested to 1.1 of the internal pressure
  3. min. and max flow rate in gas and liquid hydrocarbons should be considered
  4. do not perform hot taps in stagnant gas and liquid hydrocarbons lines
  5. Hot tap fittings (branches) should comply with ASME B31.3 (equal tee or weld out let WOL) depends on the size of the main and the branch.
  6. metallurgy of main pipe and hot tap fitting and welding electrodes should be compatible.
  7. use of low hydrogen and small diameter electrode as possible to reduce the input heat

These are some of many factors need to be considered.

Hot tap is a safe solution and very useful technology when it is done right, missing any of the above points could lead to unpleasant results.

I hope that the above clarifies the points of discussion.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Hot Tapping on Natural Gas Line

03/02/2011 8:03 AM

There should be a written Process Description document and a set of design calculations to hand that have been used to size the line. Ask the local Process Engineer for them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (2); Anonymous Poster (1); Bahaa Nasser (1); Codemaster (1); Iris (1); James Stewart (3); Just an Engineer (1); lyn (1); mech.1986bilal (2); Mikerho (1); old salt (1); PWSlack (1); redfred (3); TonyS (2)

Previous in Forum: Olympian Diesel Generator   Next in Forum: Space Saver Mechanical Hand Crank Compartment Control

Advertisement