8000A Bus Bar Size

12/12/2011 12:04 AM

Hello,

I am going to design a synchronization panel for 3 genrater sets, the genrator set haveing the capacity of 1500KW each, on voltage rating is 415V, 3Phase, 50Hz.

I want to know the size of 8000A Bus Bar.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: 8000A Bus Bar Size

12/12/2011 2:54 AM

WAG 8 in2 cross-section.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: 8000A Bus Bar Size

12/12/2011 4:13 AM

What - from scratch?

Surely an earlier design can be cloned and altered to suit?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#4
In reply to #3

Re: 8000A Bus Bar Size

12/12/2011 9:14 AM

OT???........Really???????

Not anymore.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #4

Re: 8000A Bus Bar Size

12/13/2011 9:17 AM

Respect.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: 8000A Bus Bar Size

12/12/2011 1:16 PM

Follow the international and local standards and regulations relating to your specific application and country.

If you are not qualified to perform this type of design work, don't.

__________________
jack of all trades
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#6

Re: 8000A Bus Bar Size

12/12/2011 10:00 PM

If you don't know what bus bar size to start with...you have no business designing a sync panel, or is this well disguised homework question ?? Regards, Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: 8000A Bus Bar Size

12/12/2011 11:31 PM

Try www.storm copper.com

__________________
pnaban
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#17
In reply to #7

Re: 8000A Bus Bar Size

12/13/2011 1:18 PM

Or you can try the Copper Development site:

http://www.copper.org/applications/homepage.html

Lots of info on copper usage from electrical, plumbing, and architectural.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8

Re: 8000A Bus Bar Size

12/12/2011 11:36 PM

In my opinion to operate the three 1500 kw DG sets in parallel, there is no need to have 8000 A Busbar in the Switch board

It is enough if we have bus bar capacity of 5000 A.

But you have to suitably locate the incomer and out going breakers in the switch board.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: Dec 2011
Posts: 3
#9
In reply to #8

Re: 8000A Bus Bar Size

12/12/2011 11:47 PM

Good day.

Yes you are right no need the 8000A Bus Bar in the switch board, 5000A can works, but this is client requirments.

Regards.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10

Re: 8000A Bus Bar Size

12/13/2011 12:09 AM

For one DG at cos φ = 0.8, A = 1,500,000/(415 √3/0.8) ≈ 2609. Depending on switchboard topology, the bus bars might need to carry 2609, 5218, or 8427A; with possible further correction for continuous loading.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #10

Re: 8000A Bus Bar Size

12/13/2011 12:37 AM

The previous 8427A should have been 7827A (arithmetic mistake),

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13
In reply to #12

Re: 8000A Bus Bar Size

12/13/2011 12:56 AM

When all 3 sets are feeding the common busbars,what should be the SC withstand capacity of the busbars,considering a fault in busbars or in outgoing feeder?.

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11

Re: 8000A Bus Bar Size

12/13/2011 12:32 AM

If you have no idea how to determine conductor sizes then you are the wrong person for this job.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#14

Re: 8000A Bus Bar Size

12/13/2011 1:26 AM

Sir, Please let me know you need in copper or aluminium and the outgoing capacity and numbers then only I can suggest the size of the panel.

Register to Reply
Participant

Join Date: Dec 2011
Posts: 3
#15
In reply to #14

Re: 8000A Bus Bar Size

12/13/2011 1:59 AM

Good day

Three Gen. set having the capacity is 1500KVA each and 4 out going with the full load capacity is 1800A each.

The Bus Bar we desier is copper.

Thanks & regards.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 268
#18

Re: 8000A Bus Bar Size

12/17/2011 8:45 PM

Just use a crowbar or something, it will work fine......i thynk...

__________________
guds777
Register to Reply