Air Testing of Water Lines

08/22/2013 8:28 AM

We need to air test at 50 psi for 15 minutes, the uPVC water pipes of 200 mm and above of several Kilmeters with air in order to conserve water. Is this is permissible in any standard.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Air testing of water lines

08/22/2013 8:47 AM

Define <...need...>, please.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Aug 2013
Posts: 4
#2
In reply to #1

Re: Air testing of water lines

08/22/2013 8:53 AM

This is the intension to save water. Thanks for quick response.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Air testing of water lines

08/22/2013 9:01 AM

Please explain why there is a need to test the lines.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Aug 2013
Posts: 4
#6
In reply to #3

Re: Air testing of water lines

08/22/2013 9:06 AM

Leakage test for newly installed lines

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Air testing of water lines

08/22/2013 9:07 AM

What about structural test for newly installed lines, then?

And where does the need come from?

  • A 200mm Ø line 10km long under test contains 314m3 of water, or 314m3 of compressed air, either at 50psig. Why choose the one over the other?

Keep going. Think it through.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
6
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Air Testing of Water Lines

08/22/2013 9:03 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Air Testing of Water Lines

08/22/2013 9:04 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#30
In reply to #4

Re: Air Testing of Water Lines

08/23/2013 11:15 AM

I'm going to throw in an opposing view from the crowd on this one, I say you can use air on certain applications.http://flexpvc.com/PVCPipeSize.shtml depends a lot on the schedule you use

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Air Testing of Water Lines

08/22/2013 9:30 AM

If this is going to be a water line, why are you trying to conserve water?

Is the line buried? What schedule (wall thickness) is it?

One of the problems with compressed air in PVC is that small amounts of oil that might be present can soften and weaken the PVC, which can then burst into shards like shrapnel. A one-time leak test with clean air at well below the pipe's pressure rating would not have this problem.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Aug 2013
Posts: 4
#9
In reply to #8

Re: Air Testing of Water Lines

08/22/2013 9:37 AM

The pipes are burried Schedule 80 uPVC. Intension is to save water in testing of water lines of a segment say 50 to100 meters.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: Air Testing of Water Lines

08/22/2013 9:40 AM

100m of 80mm Ø pipe is about 0.5m3.

0.5m3 @ £0.60GBP per m3 delivered is about £0.30GBP or just over half the value of a 2nd class postage stamp. Go on. Explain further.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Air Testing of Water Lines

08/22/2013 9:38 AM

After the initial flurry of activity on this thread, it's all gone very quiet, for some reason.

OK. Consider these scenarios:

  1. A Test Inspector is standing next to a 200mm Ø line some 10km long, clipboard, pencil and stopwatch in hand, while the line is being pressurised to 50psig with water. Owing to an unseen fabrication defect, when the line reaches 50psig, there is a sudden catastrophic failure and the pipe ruptures violently. What happens to the Inspector?
  2. A Test Inspector is standing next to a 200mm Ø line some 10km long, clipboard, pencil and stopwatch in hand, while the line is being pressurised to 50psig with air. Owing to an unseen fabrication defect, when the line reaches 50psig, there is a sudden catastrophic failure and the pipe ruptures violently. What happens to the Inspector?

Awaiting response.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #10

Re: Air Testing of Water Lines

08/22/2013 9:45 AM

LOL, well who cares, he got what he deserved for standing so close....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #13

Re: Air Testing of Water Lines

08/22/2013 9:46 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12

Re: Air Testing of Water Lines

08/22/2013 9:43 AM

15 minutes seems light, but it depends on who specified that and why, most leak tests are longer but it could easily be 15 minutes, why don't you just ask the person who spec'd that number??

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15

Re: Air Testing of Water Lines

08/22/2013 10:01 AM

As Tornado said, are the lines buried, or above ground?

If they are buried, and the above ground portion is wrapped with some blankets or protective material, for the test, I say go ahead and use air.

If the pipe is above ground, then I'd say maybe not.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #15

Re: Air Testing of Water Lines

08/22/2013 10:07 AM

Is there an echo in the room?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #16

Re: Air Testing of Water Lines

08/22/2013 10:12 AM

Is this the first echo you've ever heard here?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Air Testing of Water Lines

08/22/2013 10:11 AM

Here's a true story.

A long, long time ago, in the last century in fact, a much younger PWSlack was despatched to test a new-build diesel fire pump at a factory somewhere in Europe (names and locations have been altered to protect the innocent). Before the test, the three booster pumps servicing the water mains were just ticking along at about 25A on each ammeter with a mains pressure of about 55-60psig, and the Works' Chief Fire Officer, the Fire Prevention Manager and the Shift Fire Team Leader were all in attendance. All individuals donned ear defenders, as the pump was in a small building.

Said individual switched the electric pumps off and fired-up the diesel fire pump. Vrooooooooooooooooooooom! Off it went. Conversation in the building, even through ear defenders, became impossible. Pressure went up to 135psig. After a few minutes, all three got a call on their radios, which they were unable to address as the background noise was so high. After a couple of minutes more, the diesel was shut down and the electrics turned on again. Except there was a change. Current was up to 55A and the pressure was way down.

There was quite a commotion on the way back to the office, with fire appliances and other vehicles in attendance at one spot, with people running about turning valves off and running-out fire hoses to couple hydrants together.

A piece of reinforced roadway the size of a barn door had lifted and cocked itself to one side. There was water, mud, stones and all sorts of other mess everywhere from the cast iron main underneath it that couldn't handle it any more. A colleague remarked, "It was great to watch - just like in Thunderbirds when The Mole breaks through!"

Not finished yet.

In the distance, the Works Maintenance Manager is approaching, and his normally-cheerful face is bright scarlet. Uh-oh, serious uh-oh.

He approaches.

"Did you do that?", he asked, with a calmness that was unnervingly out-of-keeping with the colour of his face.

[Honesty is the best policy] "Er, yes, <first name withheld>, I did."

"Well, next time you do it, make sure I'm b...dy-well on holiday!"

There is a moral here:

  • Imagine what would have happened if the barn-door-sized piece of road was being propelled by compressed air instead....

Nuff said?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#19

Re: Air Testing of Water Lines

08/22/2013 10:20 AM

I can tell you if a joint pops it sounds like a shotgun going off....If you happen to be standing next to it and the pipe hits you in the leg, you will be limping for a few days...at least that's what I've heard....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#20

Re: Air Testing of Water Lines

08/22/2013 12:50 PM

Is this is permissible in any standard.
I doubt it. However, the only standards that apply are those applicable to your jurisdiction.

__________________
Think big. Drive small.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21

Re: Air Testing of Water Lines

08/22/2013 4:26 PM

...the location of which is unknown to the forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#22

Re: Air Testing of Water Lines

08/22/2013 6:03 PM

Ummm,

If the lines are to carrry water, why not hydrostatically test them with....

water ?

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#27
In reply to #22

Re: Air Testing of Water Lines

08/23/2013 3:28 AM

Hey - that's an idea.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Anonymous Poster #1
#23

Re: Air Testing of Water Lines

08/22/2013 9:54 PM

I think it was alleged Mr. Jacky S. Brown thought he needed to test a similar diameter pvc water line with air, and also not at very high pressure. Only he had about 300 feet of it, and thus far less energy in his bomb than you will have in yours. While sadly he is not around to confirm it was solely his idea, or why the testing could not be done more safely, see at https://www.oshrc.gov/assets/1/6/09-1158.pdf?789 that that court apparently believed it was his idea that day and agreed to vacate at least one OSHA charge against others, of creating a dangerous environment by testing pvc pipe with air.I am aware of many other similar incidents involving air and particularly low toughness plastic pipes, worldwide and going back at least three decades or so, with many serious injuries and /or fatalities involved. Air is to be respected with all vessels and pipes.The specific warning provided by SolarEagle is not idle gossip.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#28
In reply to #23

Re: Air Testing of Water Lines

08/23/2013 4:37 AM

Thought-provoking story. Thanks for sharing it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#24

Re: Air Testing of Water Lines

08/22/2013 11:30 PM

If an air test at 50psi doesn't fail and blow the ears off of everyone besides other limbs and body parts, you will not be able to find any small leaks because it will not cause a noticeable pressure drop due to the compressibility of gases such as air. If you were to use water the only body parts in danger are wet feet. Since water is not compressible, any leak will cause an immediate loss of significant pressure. You will be able to notice this.

Also when the modulus of elasticity of air, plastic and water are considered, air will expand easily. When air is heated, depending what time of the day this pressure test is done, you could end up with a higher pressure after the test than at the beginning of the test.

As I, and others have preached, air in pvc is a claymore mine waiting to explode. Water is a pair of wet socks.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#25
In reply to #24

Re: Air Testing of Water Lines

08/22/2013 11:56 PM

According to the OP, the pipe is buried.

#9

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#26
In reply to #25

Re: Air Testing of Water Lines

08/23/2013 12:13 AM

Thanks, I missed that.

Depending upon how deep he has them buried, the intensity of the sun and soil conditions it could have a minor effect, but not nearly as much as I had projected.

Thanks again!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#29

Re: Air Testing of Water Lines

08/23/2013 11:07 AM

"Is this is permissible in any standard."

NO! NO! NO! NO! NO! NO! NO! NO! NO! NO! NO! NO!

PVC pipe not to be used in compressed air systems

October 1990

The Department of Labor & Industries warned consumers and employers in May 1988 that plastic-polyvinyl- chloride (PVC) pipe cannot be used in compressed air piping systems without risk of explosion. By law, employers must protect their workers by avoiding the use of unapproved PVC pipe in such systems.

As Solar Eagle said!

Even buried I would not charge a line of several kilometers long with air.

Is this potable drinking water?

If this is a new install then you need to flush the pipe anyway!

Charge the piping with water and be done with it.

The piping should have been tested prior to burial with the intended fluid that it will transport.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#31

Re: Air Testing of Water Lines

08/23/2013 11:38 AM

I can see a problem using air @ 55psi, but normally a pressure of 5 psi is used to test a pressure vessel. It may take a longer time for leak down to occur, but it is a safe method. A typical air test, is 5psi; hold for 15 minutes; no leakage allowed. If leakage is detected, inspect, repair and retest. This is something we did on ships all the time where using water as a test medium is not practical.

__________________
Mr.Ron from South Ms.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#32

Re: Air Testing of Water Lines

08/23/2013 12:55 PM

Dear Mr.syedzaidi,

1 What is the working Pressure designed.? 2. On what basis 50 psig. air is decided.? 3. Is the pipe laid below ground.? 4. What is the class of pipe used.?

It is NOT CORRECT to use Air for testing. Only water is to be used for testing. As the pipe line is installed, the class of pipe will vary and towards the ens - the thickness will reduce and hence 50 psi Air Pressure IS NOT ADVISABLE.

I have experience of maintaining, for 14 years, 13400 Metres 250 MM AC Pipe for Water Pumping 1600 M^3 of water in 16 Hrs in a day.

Pipe laid for first 1/3 of total length was class C pipe - 15 MM thick, and second 1/3 is of B Class - 10 MM thick, and balance is A Class - 5 MM thick, where the Pressure is of 1/3 of Pressure at the delivery of the pump.

If compressed air is used - then, the presuure at the delivery end will be very near to 50 psig it will pose problem.

DHAYANANDHAN.S

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#33

Re: Air Testing of Water Lines

08/28/2013 10:42 PM

DO NOT PRESSURE TEST A WATER MAIN WITH COMPRESSED AIR, UNLESS YOU WANT TO KILL YOURSELF OR SOMEONE ELSE!!!!!!!

Follow the AWWA C600 Standard for Hydrostatic Pressure Test, as follows:

http://in-valparaiso.civicplus.com/DocumentCenter/Home/View/917

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Register to Reply 33 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CaptMoosie (1); dhayanandhan (1); Fredski (2); K_Fry (1); lyn (3); old salt (2); Original_Macgyver (1); PWSlack (11); ronseto (1); SolarEagle (3); syedzaidi (3); Tornado (2); WJMFIRE (1)

Previous in Forum: Ammonia - Is it Lethal?   Next in Forum: Emissions Analyzer

Advertisement