Can I Use 50Hz Motor on 60Hz?

10/24/2013 6:31 AM

I have motor with speci mentioned. 380/440/460V 50/60Hz. My question is whether I can use the motor with power supply 380V 60hz.

Register to Reply
Pathfinder Tags: Electrical motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Can I use 50Hz motor on 60Hz

10/24/2013 7:15 AM

Please read the spec again. What does it say?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
5
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3
In reply to #1

Re: Can I use 50Hz motor on 60Hz

10/24/2013 7:25 AM

I've just run it through my Krisdel Motorcalc program and I reckon it's ok at any of the following:-

380/440/460V 50/60Hz.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Good Answer (Score 5)
Active Contributor

Join Date: Oct 2013
Posts: 12
#2

Re: Can I use 50Hz motor on 60Hz

10/24/2013 7:15 AM

I think I'm not sure it is available to use the motor on 60Hz.but, in that case, it's power output just will be different.First of all, you'd had better consider the power output for each case.

Register to Reply Off Topic (Score 3)
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: Can I use 50Hz motor on 60Hz

10/24/2013 7:32 AM

Yes. If it drives the load on 380V 50Hz it will drive it at 380V 60Hz. Max power is unchanged (higher speed, lower torque, same current).

But on voltage 20% higher, ~ 460V, it can give 20% higher output (higher speed, same torque, same current).

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Can I use 50Hz motor on 60Hz

10/24/2013 8:33 AM

The spec clearly states that you can, however the thing that only you can see is the load that will be driven by the motor, the speed WILL be different, as will all of the critical points on the motor speed/torque/load curves. Only you can determine if this is acceptable to the load being driven or process application.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Can I use 50Hz motor on 60Hz

10/24/2013 8:46 AM

I say that the OP cannot run this motor on 60Hz power. Since the motor manufacturer clearly states that the motor is rated for this voltage and frequency but the OP is still not sure if this combination is suitable. I think that the OP should pay for an outside consultant to approve this design.

I wonder if a certain feline and rodent would be available?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #6

Re: Can I use 50Hz motor on 60Hz

10/24/2013 11:48 AM

Good suggestion.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 9:34 AM

you can understand the answer possibly a little better after reading thishttp://www.usmotors.com/TechDocs/ProFacts/50Hz-Operation-60Hz.aspx

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 10:15 AM

Yes, you can!

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 11:41 AM

Yes

Spec says 380/440/460V 50/60Hz, You are asking about 380V 60hz. The analysis of these specs and requirements, i.e. 380/440/460V 50/60Hz states that it can be done, it is built to do so, put the power on and watch it spin.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 11:58 AM

I think it's more likely a bad/sloppy nameplate design if it really says it exactly that way, or a misinterpretation of what it is really saying.

Motors are designed to put out torque. Torque output equates to the design ratio of voltage and frequency, the V/Hz ratio. A motor is typically designed with a tolerance of +- 10%, above which the windings saturate and over heat, below which the under excitement loses peak torque at the square of the voltage change, so slip increases, more current is drawn and the motor overloads.

A motor designed for 380V 50 Hz has a V/Hz ratio of 7.6:1

A 460V 60Hz design would be a ratio of 7.667:1, virtually the same.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #11

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 12:25 PM

This would not be the first time I saw a motor or any other part for that matter that specified on the component an acceptable usage range that in the manufacturer's documentation a de-rating disclaimer explained the change in operation.

Since we know nothing but the sparse information the OP provides, I still say a consultant should be paid.

Can somebody use this motor to reliably and safely move something in both 50 & 60 Hz power grids, absolutely. Can somebody else fail in using this motor in multiple power grids, absolutely. Can I tell which somebody the OP happens to be, probably not. While the OP does recognize the uncertainty of the situation, they did not provide any information for a proper analysis.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#19
In reply to #11

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 2:34 PM

I have seen this same multi-use rating on several different size motors from multiple manufacturers over the last 5 -6 years.

I was curious how the internal structure design would compensate for the heating issues so I called a couple of my old contacts that still work in the industry.

I was told that the motor stator & rotor laminations along with the rotor shorting rings and the winding span, # of turns, and conductor size have all been redesigned to offset and eliminate the heating issues.

This was done so that the manufacturer can lower costs and provide motors that can be used internationally without having two different designs and use only one assembly line.

To date I have not seen nor been made aware of any outstanding issues with any of these multi-use motors whether used here in the USA at 60HZ or at our other sites in South America, Africa, or Indonesia at 50 HZ.

I was not given any specific motor design details due to proprietary security so I cannot elaborate.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 12:23 PM

Premature postulation...

I think it's more likely a bad/sloppy nameplate design if it really says it exactly that way, or a misinterpretation of what it is really saying.

Motors are designed to put out torque. Torque output equates to the design ratio of voltage and frequency, the V/Hz ratio. A motor is typically designed with a tolerance of +- 10%, some IEC designs are +-5%. anything above tolerance and the windings saturate and over heat, below and the under excitement loses peak torque at the square of the voltage change, so slip increases, more current is drawn and the motor overloads.

A motor designed for 380V 50 Hz has a V/Hz ratio of 7.6:1

A 460V 60Hz design would be a ratio of 7.667:1, virtually the same.

A 440V 60Hz design would be a ratio of 7.33:1, still way within tolerance even if the tolerance is +-5%.

It's more likely that the nameplate SHOULD have said (or did, but it was misinterpreted):

380V 50Hz or 440/460V 60Hz. Sometimes it is only the juxtaposition of the nameplate listings that is used to attempt to make that clear, but often times that is misinterpreted as a subtlety.

If you apply 380V 60Hz the ratio becomes 6.33:1, well below even the most generous tolerance limits. The peak torque will drop to roughly 70% of what the original design was, risking that it may fail to accelerate the load before exceeding the thermal limits of the motor. Running torque drops to roughly 80%, so motor slip will increase significantly at rated load, the motor will pull more current and might overload. If the motor was over designed by 20% you may be OK, and that might be the case. But you cannot ASSume, you must ask the responsible parties, i.e. the machine designer or motor supplier.

Furthermore, you failed to mention the machine involved. If it is a centrifugal (quadratic) machine such as a pump or fan and it was designed around flow at 50Hz, the 20% increase in speed results in the motor LOAD increasing to 172% of what it would be at 50Hz, it's called the "Affinity Law", look it up. You might be able to reduce flow mechanically to compensate, but again, you must not ASSume it is OK.

Good luck.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#14

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 11:02 PM

Why not just ask the tech guy at the company who makes it?

__________________
If it was easy anybody could do it.
Register to Reply
3
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#15

Re: Can I Use 50Hz Motor on 60Hz?

10/24/2013 11:40 PM

Dear Mr. ayk538,

This Topic discussed few times earlier in this Forum. You can search here in CR4 itself.

Pl. open the link below and you will find the discussions.

http://cr4.globalspec.com/search/sitesearch?do=show&srchobjs=t%2Cc&order=asc&fs=12&sort=textmatchrank&srch=50%2F60%20Hz%20use

DHAYANANDHAN.S

Register to Reply Good Answer (Score 3)
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#16

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 8:16 AM

Yes.

You said so yourself.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#18
In reply to #16

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 9:16 AM

The motor nameplate says it can be done, but I wouldn't do it. The motor will run but will be under-excited and will have a lot of slip. It really will not hurt the motor, but it will be an inefficient use of electricity. At 460 or 480 volts it will run more efficiently but at more RPM. The people who have responded that the nameplate is unusual have not looked at very many motor nameplates. This is very common designation and means what it says as to the motor's capability to not self-destruct. It doesn't guarantee efficiency at all these ratings.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#17

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 9:09 AM

Yes you can run it, but be prepared for all the problems that could arise.

1.- The motor will run slower and hotter than at the correct frequency.

2.- Trips due to over heating can occur more often.

3.- Issues with items not operating correctly due to not having the correct RPM., etc.

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#20
In reply to #17

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 4:13 PM

Quoting Vargaalex

1.- The motor will run slower and hotter than at the correct frequency.

2.- Trips due to over heating can occur more often.

3.- Issues with items not operating correctly due to not having the correct RPM., etc.

The motor will run faster not slower. The Motor will not overheat if the volts/hertz is the same and will probably actually run cooler since the increased speed will improve cooling. The normal problems are running a 60HZ motor at 50HZ not the other way around. The answer from Vargaalex would be correct if the question was opposite of what it was. You can almost always run a 50HZ at 60HZ if you can stand the speed increase and watch volts/hz and keep the expended hp the same. You almost always cannot run a 60HZ motor at 50HZ unless the nameplate says you can, but the same things need to be watched.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#21
In reply to #20

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 4:31 PM

All true if this is a fully synchronous motor. But the common problem people find when running many 50 HZ induction motors at the increased frequency of 60 HZ is with the higher speed the mechanical load will often exceed the available torque at the higher frequency. This can induce more slip which results in a net lower rotor angular velocity than at 50 HZ. We know nothing about the mechanical load.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#22
In reply to #21

Re: Can I Use 50Hz Motor on 60Hz?

10/25/2013 8:52 PM

I was referring to induction motors only. Synchronous motors do not have ratings such as these. As long as the volts/hz ratio is maintained and rated load is kept within nameplate values your comments are not valid.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#23
In reply to #22

Re: Can I Use 50Hz Motor on 60Hz?

10/26/2013 1:07 AM

I presume that you did read the question posed by the OP. The OP wishes to use the lowest voltage rating and the highest frequency on the name plate. The volt/hz ratio will not be maintained. We also have no idea of the mechanical load. As others have already mentioned some mechanical loads (centrifugal pumps) will increase with the square of the angular velocity. An increase from 50 Hz to 60 Hz can now be nearly a 50% increase in mechanical loading. Nor do we know the NEMA torque curve for the motor in question to hazard a guess how much slip should be expected at either frequency.

So powering this motor with the high frequency lowest voltage will be electrically sound. The unknown mechanics could pose a sufficient problem of overloading this unknown motor. I agree that most designs have sufficient power and torque reserves that a problem is not likely but there can still be a problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#24
In reply to #23

Re: Can I Use 50Hz Motor on 60Hz?

10/26/2013 1:29 AM

If that would be a problem, the nameplate should have stated:

380V 50Hz/440-460V 60Hz

I.e., segregating the matching V/Hz with each other.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#25
In reply to #24

Re: Can I Use 50Hz Motor on 60Hz?

10/28/2013 12:48 PM

That's right, also I'd expect to see a voltage range for 50Hz, say 380-400V. On 60Hz (and the appropriate volts) it will produce 20% higher power than at 50Hz. OP - does the nameplate give power at both Hz?

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#26

Re: Can I Use 50Hz Motor on 60Hz?

10/29/2013 9:49 AM

As most of the respondents have mentioned, your speed and torque will be different

Being a Maintenance Technician here in the states for the last 3 decades we typically use the standard:

  • 120 v AC / 60 HZ
  • 208 / 230 v AC / 60 HZ
  • 460 / 480 v AC / 60 HZ

Anything at 50 HZ is what we call a European rating, and I have never wired a motor for 380 V 60 HZ here in the USA. I would suggest a VFD (Variable Frequency Drive) if the motor is compatible with being powered by a VFD.
Do you reside in an area where you have access to 50 HZ and 60 HZ? Where is that?
I would use the ratings from the power grid and power the motor accordingly.The higher the voltage, the lower the current draw on the grid and less money spent on electricity. I always try to power a motor with the highest available voltage.
I know, electrical discussions can be a bit confusing when you introduce too many options in it. I see on a daily basis the different voltages and ratings that manufacturers label their product with. I.E. On these contactors I have sitting in front of me, the coil voltage shows "24 V 50/60 HZ" which means it is an AC coil, the other shows "24 V" which means it is a DC coil, and the other shows "110 V 50/60 HZ" which means I will power it with 120 V AC. Also, using the designation of 120 V is the same as saying 110 V or 115 V. I'm going to be out in the field working and if I see an interesting motor plate, I will post it.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#27
In reply to #26

Re: Can I Use 50Hz Motor on 60Hz?

10/29/2013 10:18 AM

The speed will be higher on 60Hz. If voltage kept at 380 (as OP says) torque is lower (x 0.83), power is unchanged. If voltage increased by 1.2x, to ~ 460V, torque is unchanged, power is increased by 1.2x.

These are maximums the motor can output, the actual power depends on the load. I would expect the OP knows what the power drawn by the load is at 60Hz, as I assume it's a 60Hz machine, but feedback from OP would help. In that case, if the motor rated power at 380V, 50Hz is enough for the load at 60Hz, it will be OK on 380V, 60Hz.

__________________
Give masochists a fair crack of the whip
Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (3); Codemaster (3); dhayanandhan (1); Fredski (1); JCase (1); JRaef (2); lyn (1); old salt (1); Original_Macgyver (1); PWSlack (1); RAMConsult (1); redfred (4); SeZaR (1); SHOCKHISCAN (1); Tornado (2); user-deleted-1105 (1); vargaalex (1); Yusef1 (1)