Thermal Power Station

12/22/2013 6:28 AM

Hello friends, I have a question and that is " How we can increase the output power of a thermal power station" i.e let suppose its current output is 100MW and we want to boost it upto 120MW then what we have to do? Looking for a brief answer.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Thermal Power Station

12/22/2013 7:57 AM

Increase the heat.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Thermal Power Station

12/22/2013 8:26 AM

Burn 20% more fuel.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#18
In reply to #2

Re: Thermal Power Station

12/23/2013 8:34 AM

Looks like you and lyn were correct

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Thermal Power Station

12/22/2013 8:55 AM

You need a team of experts to evaluate the existing system and make recommendations that would result in a money vs increased output options, then choose the option that meets your goals....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Thermal Power Station

12/22/2013 9:34 AM

What more can I say?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#5

Re: Thermal Power Station

12/22/2013 10:36 AM

Let me guess - you are management, right?

How about "Add a 20MW thermal power station?"

Register to Reply Good Answer (Score 2)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Thermal Power Station

12/22/2013 11:12 AM

Or if you are in accounting, erase the zero in the middle and write in a two.

You are getting silly answers because it is a silly question. "Power stations" (whatever that means) would likely be designed for a maximum output capability. The rating of something like that would have nothing to do with how much less than that you are using, it has only to do with the CAPACITY. If it were capable in any way of a 120MW output, it would be called a 120MW unit, not a 100MW unit. So the answer to your question falls into two categories: complete redesign, or bolt-on addition, neither of which can be further elaborated on from a one sentence description.

"Burn 20% more fuel" however may not be any more serious than my initial response. We all know that there would be conversion losses, so it would likely be more like "Burn 37.43% more fuel." ;)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #6

Re: Thermal Power Station

12/22/2013 12:14 PM

JR,

There was a bit of whimsy/sarcasm in my answer, I thought about adding an additional 3-5% to account for the increased losses but then I thought that such an unthinking question required an equally unthinking response.

Alan

btw- overall heat-rate tends to go down as plant size increases; i.e., the efficiency gets incrementally better, not worse.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21
In reply to #8

Re: Thermal Power Station

12/23/2013 12:24 PM

"There was a bit of whimsy/sarcasm in my answer,..."

I understood that, tried to respond in kind, but I can't get emoticons to work on my ad in this site ...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Thermal Power Station

12/22/2013 11:37 AM

Build it larger in the first place.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Dec 2013
Posts: 2
#15
In reply to #7

Re: Thermal Power Station

12/23/2013 2:50 AM

Thanks friends for your feedback. And moreover this increase in output falls within the capacity of the plant which i hadn't mentioned previously. anyhow thanks once again to all of you.

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#17
In reply to #15

Re: Thermal Power Station

12/23/2013 8:33 AM

Then the brief answer is "increase the load."

PS: You still haven't 'mentioned' the capacity of the plant.

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Lucknow , Uttar Pradesh , India
Posts: 15
#9

Re: Thermal Power Station

12/22/2013 1:15 PM

Add a 20 MW Turbine...

__________________
Mukesh Kumar
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10

Re: Thermal Power Station

12/22/2013 1:17 PM

There is no brief, accurate answer to this question.

Many engineering laymen do understand that any machine is designed to slightly exceed their specifications in order to meet these specifications. What few laymen understand is when one exceeds the stated specification there is always a price to pay somewhere. How big of a price usually depends on the length of time that one exceeds the specification. If the time period is measured in seconds or fractions of a second then the price can just be the price of replacing machine protection devices.

What baffles many laymen is that a modest boost in performance can be apparently achieved with little immediate impact. Usually the impact happens in the Mean Time Between Failures (MTBF) across the whole machine in this scenario. An apparently modest boost to 10% above rated performance can easily reduce the MTBF to 1/10 of it's previous value. So a machine expected to last 10 years may now fail in only one year.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: Apr 2009
Location: crankshaft producing hub in belgaum,karnataka,india
Posts: 38
Good Answers: 1
#11

Re: Thermal Power Station

12/22/2013 10:07 PM

Dear Friend.

To achieve something you have to sacrifice something .

In the first place, you can increase the combustion rate of fuel by addition of a turbocharger accompanied with Oxygen gas, to be forced into the furnace. this can increase the heating rate of your power station and inturn efficiency.

But the economics of using the turbo charger and oxygen have to be considered and I feel it will solve your problem.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#19
In reply to #11

Re: Thermal Power Station

12/23/2013 9:52 AM

Dear Mr.ravi bagewadi,

I am afraid that mere additional heat release in the furnace alone is not the solution and it will create problem. The heat released should be transferred by the Boiler Tube Heating Surface, which has got a SPECIFIC HEAT TRANSFER RATE and variation will be marginal and it will not handle 20% more as stated in the original post.

If heat is not transferred by the Heating Surface and absorbed by water, the Furnace Temp. will GO UP, Super Heated Temp. of Steam will shoot up, Heat Loss through Stack Gas will go up etc. Higher Furnace Temp. will lead to Travelling/Dumping Grate problem, Melting of Ash etc.will occur.

Possibility of adding ADDITIONAL HEATING SURFACE, ECONOMISER, SUPER HEATER etc. should be studied by a COMPETENT AUTHORITY.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12

Re: Thermal Power Station

12/22/2013 10:39 PM

use waste heat recovery,economiser etc

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#32
In reply to #12

Re: Thermal Power Station

01/06/2014 7:34 AM

That would only increase the efficiency, and not the rating.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#13

Re: Thermal Power Station

12/22/2013 10:42 PM

Read the text that you would have been given for this assignment - or attend more lectures.

__________________
johny451
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#14

Re: Thermal Power Station

12/22/2013 11:04 PM

Get a bigger/additional boiler.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#16

Re: Thermal Power Station

12/23/2013 4:16 AM

Dear Mr.shazhadkhan,

Your question and that is " How we can increase the output power of a thermal power station"

It needs a thorough study, on all front including, Boiler, Steam Line Capacity, Turbine Capability, Alternator Capcity,Electrical System, etc., etc.

The lowest capacity in the system will decide the real capacity, if any, available.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#20

Re: Thermal Power Station

12/23/2013 11:33 AM

Looking at your post #15, it appears that the problem is that the plant is performing below design specification. Somewhere in the process there is/are one or more bottlenecks. You should be able to check the rate of fuel burn and combustion air delivery against design, pressure and temperature of the main steam line but beyond the obvious, you need experts in the various disciplines.

Have tried asking the operators? they may have the answers, but, I'm sorry to say, managements often think it is below them to ask for knowledge from the people they supervise.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#22

Re: Thermal Power Station

12/24/2013 10:27 AM

I think it is more complicate.First of all the overload for a limited duration may be permissible for most of turbines and boilers-the generator is built for overload-usually.I don't think you need overloading except in peak hours.I saw for 2-3 hours even 50% overload.

See[for instance]:

http://www.energy.siemens.com/br/pool/hq/power-generation/power-plants/steam-power-plant-solutions/coal-fired-power-plants/USC-Steam-Turbine-technology.pdf

or Google "Turbine and boiler permissible overload"

__________________
Julius
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#23

Re: Thermal Power Station

01/02/2014 10:16 AM

Instead of a conventional cooling tower that simply consumes auxilliary power, get yourself a real engineer, and build an AVE (atmospheric vortex engine). This can recover energy from low-grade waste heat (hot water from condensing steam for example, and maybe stack heat), generates a stationary vortex (cyclone) that goes way up in the air, generates a great deal of convection of local air at the ground level, and turns wind turbines attached to the AVE structure. You will still get to cool off the process. If the AVE recovers 20% of the waste heat (which is about 60% of the heat used in the first place), then the power output of the plant just went up 30%. Good math.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#24
In reply to #23

Re: Thermal Power Station

01/02/2014 5:47 PM

Wow James, why don't you just put a turbine in the stack and use the flow of hot air to turn a turbine?? Aw shucks, that would cause a restriction in the stack and increase the back pressure into the boiler which would upset the mass flow rate through the boiler and cause problems with the fuel management/pollution control computers, etc.

Seriously though, if you use hyperbolic cooling towers the only auxiliary power required is to pump the water through it, the shape of the tower creates a totally "free" convective flow of air, something that would be severely curtailed if you placed any restriction (your turbine) at the outlet.

Utility engineers have studied these type of problems for years, and are pretty damned good at getting the most bang for the buck. After all, when you design something to operate 250,000 hours you really do try to reduce your hourly operating costs.

It always angers me to see how much waste heat is produced in a typical plant, but the laws of physics and thermodynamics usually make it uneconomic to go chasing all those low-grade BTUs (but I do like combined cycle plants).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#25
In reply to #24

Re: Thermal Power Station

01/03/2014 10:37 AM

I don't think you should laugh at the AVE idea too much. I agree this is new stuff, and maybe not mature enough to be out there yet, but there are plans (I have seen them) for such a critter to be installed on the cooling side. Since the AVE creates a local vacuum (tornado like vortex), I doubt there will be a performance problem, since I have been aware for a long time "there is no gravity, the earth sucks". That's a joke, son.

If steam turbine back-pressure increased by 0.5" Hg by using this AVE device (I have no idea that it would be this much if at all), steam turbine output would suffer some small percentage, but if you get back +30%, then you have a wild increase possible in plant output, without installing a new unit.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#26
In reply to #25

Re: Thermal Power Station

01/03/2014 1:59 PM

James,

Yes, the AVE is an interesting concept, but no, it has not been proven that the vortex will continue once any restriction is put on the inlet air. All the modeling and testing "prove" what is already known, that convection creates rising air currents, the "twist" here (pun intended) is that instead of smooth laminar flow, a vortex is created.

As I said earlier, hyberbolic cooling towers do the same thing without the vortex. Any restriction at the cooling air inlet reduces the velocity of the air through the tower. Put a fan down there and it will turn, try and take and take power off that fan/turbine and it will slow down as it is loaded up. That restriction will reduce the amount of air passing through the tower and its effect will ripple back through the boiler system. It appears they are accounting for this, that's why they have set their goal at 20% recovery.

But just remember, if they draw off 20% of the cooling flow, then the energy for that 20% gain has to come from somewhere, and that "somewhere" is the fuel that made the water hot in the first place. The forces moving the air do not magically come out of the atmosphere, they come out of the temperature difference in the air column, and that comes from the heat input from the fuel that was burned. There are no free lunches at the Carnot Cycle shop, sorry, dad.

Alan

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#27
In reply to #26

Re: Thermal Power Station

01/03/2014 2:13 PM

When waste heat can be used as is then co-generation uses can be beneficial. The classic example is the heater core of an automobile in winter.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#28
In reply to #27

Re: Thermal Power Station

01/03/2014 2:58 PM

Red,

"...The classic example is the heater core of an automobile in winter...", that's simply rejecting the heat in a different place. On the other hand if you were to try and use that heat to drive an ORC (Organic Rankine Cycle) turbine and generate additional power for the batteries in your hybrid, that would be a fine example of co-generation.

Alan

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#29
In reply to #28

Re: Thermal Power Station

01/04/2014 11:30 AM

When and if....cogeneration....district heating.... all of these are noteworthy ideas, but it is extremely site specific as to the relevance or potential for success.

AVE - the idea is not to restrict air flow, and the vortex will still operate off 80% of the waste energy not recovered. Hey even if they can only do 10% (way conservative estimate), then the power plant will still gain in production by 15%:

10% of 60% is 6%. 6%/40% = 15%. We can all take a deep breath, and relax, and see if anything comes from it.

BTW - check out RAMGEN's new constant volume cycle gas turbine. (off topic, but a valiant step in making generation more affordable/efficient. Also will run off dilute sources of methane (lean premix, operates near the burn instability point more easily than normal Brayton cycle).

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#30
In reply to #29

Re: Thermal Power Station

01/04/2014 1:36 PM

James, It appears that you're well intentioned and familiar with technology, but when you say "...the idea is not to restrict air flow..." I'd like to know how it extracts energy from the air flow. Once you put anything, your hand, you, a fan, in the path of moving air (or any medium for that matter), you have altered the air flow, and if work is extracted from the turning fan, then the air has to give up some energy to do some work overcome the restriction. In the case of the AVE, the "thing" that makes the air move is the change in temperature from the bottom to the top of the vortex, and that change in temperature comes from the fuel source that is feeding it. Unfortunately reducing the air flow makes the temperature of the water returning to the condenser go up which makes the vacuum go down and the output of the turbine goes down as well. I'll check out RAMGEN (I wonder why I like the name) when I have a better internet connection, thanks for the lead. Alan

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#31
In reply to #30

Re: Thermal Power Station

01/04/2014 2:01 PM

Still remains to be seen how plant cooling efficiency is affected (good or bad), as a better designed cooling tower may be in the offing for plants that would consider this.

Yes, there is a loss of the potential, but that is what happens to any energy conversion from thermal to mechanical to electrical. Nature of the beast. IF the turbine (steam side) loses 1-2% as output, but the overall plant gains 15-30% total output, how is that a bad thing?

If the RAMGEN thing works out, it might well be moot to be discussing (1) cooling towers at all, or (2) combined cycles, or (3) cogeneration...maybe.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); bigg (3); dhayanandhan (2); James Stewart (4); Johny451 (1); JRaef (2); lyn (1); mukeshkumar5609 (1); old salt (1); passingtongreen (1); pnaban (1); PWSlack (1); RAMConsult (6); ravi bagewadi (1); redfred (3); shahzad khan (1); SolarEagle (1); Tornado (1)

Previous in Forum: Choosing Capacitor   Next in Forum: Heater Design

Advertisement