Calculating Power Supply Capacity

10/26/2009 8:14 AM

Hi all, please help me with that when I am calculating a power supply capacity what should I take into consideration? Maximum of Facility Normal Running Load (i.e. 100% of running loads + 30% of intermittent loads) or Peak Load (i.e. 100% of running loads + 30% of intermittent loads + 10% of standby loads). I presume that is Peak Load, but still have some doubts. Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Calculating a power supply capacity

10/26/2009 8:33 AM

Size it for peak loads, or it will trip out on overload during them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2008
Location: Dubai, United Arab Emirates.
Posts: 38
#2
In reply to #1

Re: Calculating a power supply capacity

10/26/2009 9:11 AM

Hi, Thanks a lot for your reply.

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#3
In reply to #1

Re: Calculating a power supply capacity

10/26/2009 9:22 AM

As PWSlack rightly says size it for the peak load. But keep in mind that while taking the 10% of the standby loads we should match it with the largest rating of the standby load and in case the 10% calculated value is lower then the largest standby load then we should take the value of the largest machine in our calculation.

__________________
Atlas Shrugged - JGD
Register to Reply
Associate

Join Date: Aug 2008
Location: Dubai, United Arab Emirates.
Posts: 38
#4
In reply to #3

Re: Calculating a power supply capacity

10/26/2009 1:16 PM

Hi Current Maarey, you are being really very supportive for guys like me who wants to learn. you have answered more than half of my total questions. First of all I would really thank you very much for that. It is really a good motivation for guys like me who wants to learn. Thanks again.

So we have to take into consideration the value of whichever is high, either 10% of the standby loads or largest machine.

Please check whether my understanding is right.

Thanks again.

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#5
In reply to #4

Re: Calculating a power supply capacity

10/26/2009 11:53 PM

Your understanding is correct

10% of the standby loads or the biggest standby load

__________________
Atlas Shrugged - JGD
Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#6
In reply to #4

Re: Calculating a power supply capacity

10/26/2009 11:59 PM

Bulls eye.

10% of the total standby loads or the biggest standby load

__________________
Atlas Shrugged - JGD
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Calculating a power supply capacity

10/27/2009 11:06 AM

There is no definitive rule to calculate the electrical loads. I worked in various projects and each of the projects follows different type of calculation. The most common method I found is:

(1) Find the rating of the connected loads (preferably name plate rating) including the future loads that are known.

(2) Estimate the duty factor (the duty factor of a motor refers to the on-time of the motor versus the total time. For continuous load, the duty factor is 1; for standby load, the duty factor is 0, for intermittent load, the duty factor may be considered 0.5 or in between 0 to 1. If an intermittent load is likely to be run during the peak period, consider it 1).

(3) Estimate the loading factor for each of the loads (loading factor is the average load divided by the peak load, over a period of time. If a 50 kw motor's average load is 40 kw, the loading factor is 0.8).

(4) Multiply each connected load (from 1) with duty factor (from 2) and loading factor (from 3)

(5) Sum up all the loads (found in 4) to obtain the total load

(6) Multiply the total load (found in 5) with 1.2 (considering 20% reserve capacity) to find the estimated calculated total capacity.

It will be helpful to prepare a spread sheet using the formula with this logic to calculate the total capacity.

Go to the recent discussion http://cr4.globalspec.com/thread/43104/Electrical-Load-Calculations and it will also help.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: Dec 2008
Location: Anthem, AZ
Posts: 392
Good Answers: 8
#8

Re: Calculating Power Supply Capacity

10/27/2009 11:13 AM

Peak loads are the key. This URL leads to a very good application note on measuring peak power losses on Switched Mode Power Supplies (SMPS).

http://www2.tek.com/cmsreplive/tirep/15774/54W_23880_0_2009.07.23.13.09.39_15774_EN.pdf

It also covers magnetic losses.

Register to Reply
Associate

Join Date: Aug 2008
Location: Dubai, United Arab Emirates.
Posts: 38
#9
In reply to #8

Re: Calculating Power Supply Capacity

10/28/2009 12:20 AM

Hi, Thanks all of you.

Register to Reply