I have tested rotor of 30 MW gas turbine 2-pole generator and the results are as under:
Insulation resistance = 33,882 Mohms
Dielectric absorption ration (IR60 second/IR30 second) = 1.10
PI = 1.46
Dielectric discharge ratio = 0.66
I would like to know the minimum acceptable DAR and PI values for healthiness of the generator rotor.
Re: PI for generator rotor
11/05/2009 4:43 AM
What does the original equipment manufacturer's operation and maintenance manual have to say on the topic?
11/05/2009 5:00 AM
As per GE - A field index (PI) of 1.25 would suggest a clean, dry field winding.
Good Answers: 244
11/05/2009 4:27 PM
(1) Dielectric Absorption Ratio (DAR) = (IR 60 seconds / IR 30 seconds)
Recommended DAR values
DAR Values
Result
Less than 1.1Bad
Between 1.1 to 1.5Good
More than 1.5Excellent
(2) Polarization Index (P.I) = (IR 1 minute / 10 minutes)
Recommended minimum values of PI for all machine components insulation classes per IEC 60085-01:1984 or IEEE Std 43-2000
Thermal class rating
Minimum PI
Class A1.5
Class B2.0
Class F2.0
See the following links:
http://www.termogram.com/articulos/Understanding_Insulation_System_Testing-Don_Shaw.doc
http://www.coleparmer.com/techinfo/techinfo.asp?htmlfile=AEMC_insulation.htm