Generator Undervoltage Condition

11/13/2009 4:42 PM

Do we trip the generator on under voltage( 27 element) condition? doesn't the voltage regulator has to take care (control) of it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2009
Posts: 20
#1

Re: Generator Undervoltage Condition

11/13/2009 9:45 PM

yes

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Generator Undervoltage Condition

11/14/2009 2:18 AM

If one can fully trust the AVR then one doesn't need a U/V Relay at all. U/V Relays are needed to detect and act during abnormalities such as failure of AVR to maintain the terminal voltage.

However, the situation is not so alarming that it calls for a trip and shut down of the generator. Only an alarm will do.

However with today's numerical relays, you can set two levels of settings for the U/V condition, one for an alarm, say at about 80% and another level for trip, say at about 70% of the rated voltage.

Register to Reply