Heat Exchanger Problem

08/16/2012 1:55 PM

Our company's maintenance department wants to upgrade a plate heat exchanger to a shell and tube. I will give you some preliminary information.

There are a number of reasons for this, there is a high degree of fouling from the product we are running, and mounting a vertical S&T would ease the cleaning. And that is the biggest reason

The issues here:

  • The viscosity of the product is high, so the flow in the shell and tube is laminar. I am currently having the product analyzed to verify the viscosity.
  • We have a temperature cross, having this would be typical for a plate and frame application.

I had written a shell and tube specification program, which from empirical information is quite accurate.

And I was running a number of scenario's. One, if I can induce a turbulent flow through the tubes, the S&T will work.

Not getting into the thermal and mechanical properties of the product.

My question is,

Has anyone had any experience with tube inserts to create/induce a turbulent flow in a shell & tube hx?

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#1

Re: Heat Exchanger Problem

08/16/2012 5:16 PM

No experience. But if you know you have a fouling fluid and use inserts, aren't you setting up a maintenance nightmare?

Ordinarily, the fluid with the controlling fluid coefficient is put on the shell side. I would assume this would be your process fluid. Is there a reason this could not be done? Also, have you considered a scraped surface heat exchanger?

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #1

Re: Heat Exchanger Problem

08/17/2012 8:41 AM

Thanks for the responses, hope I can keep a flow for my responses without going all over the board.

bigg

We already have a nightmare with a plate. It does the job, which is the first criteria, but the maintenance is the nightmare.

By removing the plates, each plate has a gasket, and to clean each plate and reassemble them... in the correct order is not very efficient.

With the thinking of a Straight through counter-flow shell and tube (Not a U-Tube), it would be mounted vertical, the tabulators can be pulled, and a brush run through on the tubes. and the buildup drop out the bottom.

See Pictures. As far as the buildup to the tabulators, they can be cleaned periodically, leave it to maintenance discretion.

The product fluid is on the tube side, but we had discussed of running the fluid on the shell side, but with the type of process we are running, the buildup would not allow this.

As far as a scraped surface, it's usually used for high viscous material. I had questioned the Viscosity of the product from the 20 year old data, and sent a sample to our lab for analysis. turns out to be a fraction of it.

We may still try the tabulators.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Participant

Join Date: Jan 2010
Posts: 2
#2

Re: Heat Exchanger Problem

08/16/2012 11:03 PM

To match a S&T thermally to a PHE will be challenging. It can require up to 10 times the surface area in S&T to do the same heat transfer. And there is also the temperature approach...the best you can hope for is 10F approach in a S&T. Look at using a spiral plate heat exchanger. They are very good on viscous, debris laden, fouling fluids.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#8
In reply to #2

Re: Heat Exchanger Problem

08/17/2012 8:43 AM

hexguy

Yes, for this application the efficiency is not good for a shell and tube. and a plate is more appropriate. Only looking at the shell and tube to cut down on the maintenance

So, I'm going to running it in my heat exchanger program with the latest viscosity, I feel with the lower cP it's going to creates a turbulent flow in the program, even though the program shows it possible, there is still a chance it could be flawed. It's been known to do that time to time with low flow and a tight temperature differential. (I know what I stated earlier about the program, was hoping the lab showed the viscous was high)

I can get a turbulent flow, with this now said, I still have to deal with the temperature cross over, The thought is hooking a series of shell and tube together, each with its separate cooling supple to avoid temperate cross over.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#14
In reply to #8

Re: Heat Exchanger Problem

08/17/2012 9:24 AM

You should be able to build a 1 tube/1 shell pass exchanger to handle the temperature cross. Depending on temperature and materials, you may need some expansion device. Good luck.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: Heat Exchanger Problem

08/16/2012 11:11 PM

I have experience with fouling flow through a horizontal T&S exchanger.

We incorporated a reversing valve that was activated by a pressure drop sensor.

It required a 4 way valve and a dump to waste drain during back flush.The back flush duration was set by a timer.

This system worked well for many years, extracting 13 Million BTU/Hr from waste water in a dyeing operation.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#9
In reply to #3

Re: Heat Exchanger Problem

08/17/2012 8:46 AM

Thanks, but I don't believe a backflush would work on a plate, it has to be manually addressed.

I'll drop some more mechanical properties on you. The brix is quite high on the product.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Heat Exchanger Problem

08/17/2012 1:34 AM

Tube-in-tube could give the temperature cross, but would tend to be large and expensive.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#10
In reply to #4

Re: Heat Exchanger Problem

08/17/2012 8:48 AM

Thats correct, and the cost/benefit is what I'm determined now.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#5

Re: Heat Exchanger Problem

08/17/2012 2:17 AM

This has started me wondering about some alternatives.

What're the working fluids?

Are they Al alloy compatible?

Pressures?

I did the thermodynamics testing and data acquisition on a "new" invention about 25 years ago. It's an alloy extrusion and has impressive heat transfer numbers.

Can't quote 'em now. Passed all the data on to the owners on completion of the tests.

It was for a local company called Thermo Dynamic Industries Pty Ltd.

Looked for a website, but can't find it to direct you to, however, DO know the guy who's boss and can put you in touch if it'll help.

When I was involved it was the start of a very good idea for some applications.

Did some work on adding spiral turbulators into HX tubestacks to increase the heat transfer.

This was on cupro-nickel tubing and had to be careful not to reduce the cross-sectional area too much. Anchoring the little devils was a challenge too. didn't want vibration causing abrasion damage withing the tubes.

Pressure drop was in the order of double, bearing in mind that we were operating at little more than ambient pressures. Increased pressures would reduce the effect.

Be interested to know how you fare with this one.

Cheers,

Stu.

__________________
"Nothing, is as it seems." Dr Wally.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#11
In reply to #5

Re: Heat Exchanger Problem

08/17/2012 8:55 AM

I can answer what I can, but it look like it's not applicable.

and I have to answer ambiguously, it is proprietary information,

What're the working fluids? Product, Pyrolytic Acid, other that that, it proprietary information, Cooling media Water from cooling tower, this summer it got up to 85F, we don't have a problem in the winter.

Are they Al alloy compatible? No

Pressures? about 60 PSI

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#13
In reply to #11

Re: Heat Exchanger Problem

08/17/2012 9:07 AM

Thanks for that.

Cheers,

Stu.

__________________
"Nothing, is as it seems." Dr Wally.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#15
In reply to #11

Re: Heat Exchanger Problem

08/17/2012 1:14 PM

Why not just get rid of the plate frame / shell and tube and cooling tower and install a evap condenser type of tower in place of all. Still using the water as your cooling media and you may have room in the tower area for an increased foot print if necessary.

you could install a VFD on the tower to control fluid temperatures, or remove all and install a air over fluid cooler in the tower area with drives on the fans as well.

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 2 for Off Topic
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#16
In reply to #15

Re: Heat Exchanger Problem

08/17/2012 2:55 PM

like to keep the change over under $100,000.

I don't know what you mean by:

and install a evap condenser type of tower in place of all.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Heat Exchanger Problem

08/17/2012 3:12 AM

Scraped surface heat exchangers might be a better way to go.

Arrange some pilot-scale trials with a vendor using off-spec product, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#12
In reply to #6

Re: Heat Exchanger Problem

08/17/2012 8:57 AM

Thanks,

Scrape surface would be considered until the lower cP came back from the lab.

And we are running some trials inhouse to atleast determine a reference.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#17

Re: Heat Exchanger Problem

08/17/2012 9:08 PM

There some very good heat exchanger manufactures out there that have every good R&D labs in house. Give some of these folks a call and let them give you a hand to come up with a proper solution. Rather then get something from me or someone else that may or may not work for your application.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#18
In reply to #17

Re: Heat Exchanger Problem

08/17/2012 9:37 PM

Darned good advice there.

Vendors are the ones with a vested interest in giving you a solution.

With a budget constraint, not a trivial amount either, solutions that are available and known to work are the most cost effective as they will work...hard to justify the cost of a trial that went wrong even if it could have been less costly, if you get my drift.

Vendors are the ones who have their fingers on/in the extant solutions. They can also come in and look at your set up if they are local.

Phoenix911 has received some excellent suggestions here. This will make him a very informed consumer.

Cool discussion, much enjoyed.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#20
In reply to #18

Re: Heat Exchanger Problem

08/18/2012 10:16 AM

I read your post after what I posted earlier which is inline, yes it is interesting.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#19
In reply to #17

Re: Heat Exchanger Problem

08/18/2012 10:12 AM

Thanks,

I'm not doing this alone, I do have a manufacturer working with me that is a leader in this, but when you have a temperature cross over, low flow and such, it is, as a thermal leader they are admit its difficult.

And some of your responses match their initial ideas. I should have some more information from them next week.

Look it it as brain storming.

I find when an issue like this comes up, the more I understand, the better chances I can come to a solution. I tend to look at cr4 as a resource, arrogant of me..... Maybe. But still a good resource.

So while they are working at one end, I'm working separately. Then we compare and come up with the best solution.

Thanks again.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#21
In reply to #19

Re: Heat Exchanger Problem

08/18/2012 11:36 AM

Perfect.

__________________
Difficulty is not an obstacle it is merely an attribute.