Transformer Question

12/11/2013 11:55 PM

Hi,

As we know that step up transformer is stepping up the voltage low level to high level in this time current will be goes down and hence primary ,secondary current will be different.If am stepping up 110 vac 1 phase by using 30va transformer then its primary current is 0.27 and secd current is.13 if it,s correct then how much load i can connect to the transformer secnodary

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#1

Re: TRANSFORMER

12/12/2013 12:17 AM

HOME WORK ALERT!

You need to pay attention in class and if you do not understand something then you should ask the instructor, they can explain it easier in person.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: TRANSFORMER

12/12/2013 2:00 AM

The answer is in the question and needs only basic arithmetic to squeeze it out. Good luck with that.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: TRANSFORMER

12/12/2013 2:23 AM

Even easier than that, it needs only copying the correct number.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#4

Re: TRANSFORMER

12/12/2013 7:35 AM

'....how much load i can connect to the transformer secnodary....'

.

How much do you have available?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Transformer Question

12/12/2013 6:06 PM

The correct answer is "only as much as the circuit protective device(s) can sustain".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Transformer Question

12/12/2013 10:15 PM

400A fuses?

The transformer goes first, cables second. you'll not blow the fuse.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#7

Re: Transformer Question

12/12/2013 11:27 PM

load it to 30va

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #7

Re: Transformer Question

12/13/2013 4:30 AM

load it to 30va MAX at 100% duty cycle at 20C`.

Can go higher/hotter for shorter duty cycle with olfactory protection on standby.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8

Re: Transformer Question

12/13/2013 12:03 AM

Put a 100watt bulb on the secondary (was primary) winding and plug the primary (was secondary) into a 120v source. The equivalent of the quantity of lumens produced by the bulb is the answer. Cool White bulbs are preferable. Remember that 1.8oF = 1oC and 1 watt-hour = 3.141394026 BTU's

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Off Topic
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#10

Re: Transformer Question

12/13/2013 5:13 AM

". . . secd current is.13" ??

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#11

Re: Transformer Question

12/13/2013 9:40 AM

Here's something to remember for your classes: Transformers cannot create or consume Power, so the total Watts going in equals the total Watts going out.

Also good to remember is the mnemonic PEIR. This word encompasses both Watts's Law (P=E*I) and Ohm's Law (E=I*R).

(You might be using V for Voltage, the symbol E stands for 'Electromotive force' the term that was used before Volta got it named after him. Besides, PIER is easier to remember than PVIR.)

Good luck with your classes, and when you get into industry, the math gets a lot simpler, you're normally stepping voltage DOWN from the power line to the equipment level, and the stock transformers come in fixed sizes, so you just have to worry about making sure your circuit protection is selected correctly, and since the fuses and circuit breakers are also in fixed sizes, it's simple addition; add up all the loads, then pick the smallest breaker that is larger than that sum. make sure that breaker is installed 'downstream' of the transformer (between the transformer and the components) and you've got the transformer protected from overcurrent. Then to find the current load on the upstream side, you simply divide the downstream current load by the transformer step-down rating. (For example, if you are using a 2:1 step-down transformer to go from 220VAC to 110VAC, and the current drain on one 110 side is 4.8 amps, the current the transformer will need on the 220 side is 2.4 amps.) Then you simply pick the smallest current protection that is greater than the load, just like on the downstream side. You would also want to make sure the transformer is rated for the total power, measured in Volt-Amps (Volt-Amps are like Watts, but there are some differences you'll learn about in the advanced classes) The 2:1 transformer I described above would need to be rated for at least (110V*4.8A) or (220V*2.4A) = 528VA.

Good luck with your studies.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#15
In reply to #11

Re: Transformer Question

12/15/2013 10:30 PM

'....Here's something to remember for your classes: Transformers cannot create or consume Power, so the total Watts going in equals the total Watts going out.....'

.

Hmmm. Yeah. Remember that for classes, because that is where it should stay. Warm humming transformers here in the real world continually nosh a little bit of whatever power they are working on.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#17
In reply to #15

Re: Transformer Question

12/16/2013 9:14 AM

Of course, ALL components consume some power, but when dealing with schoolwork, the instructor is looking for the correct math answers, and the formulae all assume 'ideal' components: All wires are zero ohms per mile, all batteries have zero internal impedance, all current sources have infinite voltage available to drive the circuit, etc.

Let the kids learn the math, THEN teach them that there real world doesn't quite line up with the math, THEN teach them how much of a 'safety factor' do build into their designs so that the final result will be 'close enough' to the math to work safely and efficiently.

Remember, you start building a pyramid by laying the foundation, you can't start with setting the capstone.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#18
In reply to #17

Re: Transformer Question

12/16/2013 10:15 AM

Oh good! I'm glad I trusted my instincts. I was pretty sure you had just made an initial typo when you actually meant to write: 'transformers do consumer power, meaning total watts going in is greater than total watts going out.'.

.

Glad we got that all sorted out.

.

I don't know very much about building pyramids at all, so I'm going to defer to you on that subject. The transformers should behave the same in a pyramid as any other structure.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#12

Re: Transformer Question

12/13/2013 4:22 PM

Put as much load as you want. It will reflect back to the primary. You cannot drive more current through a fixed load without raising the voltage, and the voltage on the secondary is fixed.

Are you asking this on a cell phone as you are writing the exam?

Just curious....

__________________
If it was easy anybody could do it.
Register to Reply
Active Contributor

Join Date: Dec 2013
Location: Dubai
Posts: 11
Good Answers: 1
#13
In reply to #12

Re: Transformer Question

12/15/2013 1:13 AM

No Mr.yusef1 am not writing any exam

In our state in electrical distribution if voltage is down means electricity board will put one transformer i just want to know how they calculating parameters for that transformers.Can you help me (you just take it as 230v ac 50Hz single phase system)

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#16
In reply to #13

Re: Transformer Question

12/16/2013 8:12 AM

Parameters are based on your load. If you increase the load on a secondary by, say, switching on more lights, you WILL increase the amperage (load) on your primary. Voltages will stay fixed.

If you use enough load to drop the voltage, you are overloading your transformer. In normal use, it might go down a volt (maybe) because of copper losses.

Yusef.

__________________
If it was easy anybody could do it.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#14

Re: Transformer Question

12/15/2013 4:51 AM

Are you sure it is 30VA and not 30kVA?

30VA is very light for your vaguely hinted application.

30 VA is like 30W...not much at all, 1 2ft fluoro and a phone charger...

Tell us more please. What loads do you want to support?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers: