We
are facing problem in operation of AC Motors. We have many flange mounted AC
motors of 315 KW,FLC-531 Amp and RPM 1475, Siemens make . Motors are connected
with star-delta starters. We are using CT operated relay of siemens for over
load protection in phase . CT range is 250-400 amp . 250 Amp is equal to .625
and 400 equal to 1 amp and mounting relay range is .625-1 Amp. Relay is mounted
upon of CT set.Problem is that motor runs normal till many hours but any time
it tripped by O/L while current does not exceed till maximum setting. O/L
setting is on .75 amp but when we check secondary current of CT than we found
1.1-1.7 amp while primary current is near about 100-120 amp, measured by clamp
meters. Than how is possible this . If output is false than why not relay
tripped in some time. we have replaced CT and Relay also one by one with new
one but problem is same. Secondary current is not proper. Kindly guide us what
should we done ....
>