VCB Tripping

08/08/2014 6:42 AM

I have commisioned a 11 KV, 630 A VCB for supplying a 315 KVA 11/.440 KV Transformer.The Transformer is getting supply from a RMU. The problem is on giving the power to the Transformer through VCB,the VCB Trips.We have checked the megger readings,all loose connections,and all possible things,we also had disconnected the transformer output connection,but still VCB trips.what can be the cause of tripping of VCB.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: VCB Tripping

08/08/2014 8:19 AM

breakers fail too

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: VCB Tripping

08/08/2014 8:35 AM

What make is the VCB?

Is it not giving any indication as to why it trips?

I've just looked at http://cr4.globalspec.com/thread/96373 Employ an engineer because you clearly don't know what you are doing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: VCB Tripping

08/08/2014 8:35 AM

The circuit breaker may not be be correct for the application or the trip settings are not correct.

Transformers and motors require a longer trip time setting to allow for the higher inrush current during energization.

You need to collect all of the information on the transformer nameplate then contact the breaker manufacturer service department and ask if you have the correct breaker.

If the breaker is rated for your application, the breaker manufacturer can determine the correct trip setting for your application.

Keep in mind that most companies have system protection setting standards and it would be a good idea to make sure the settings are in compliance with policy.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: VCB Tripping

08/08/2014 8:08 PM

Why don't you rack out the VBC to the maintenance position and test your VCB again. If the VCB does not trip that mean your VCB to your transformer OC or EF setting values are not correct.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: VCB Tripping

08/08/2014 11:18 PM

VCB trips due to inrush current . Inrush current will be approximately 10 times full load current and this will be for 100 milli sec.The over current relay provided in the VCB should be appropriately set

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#8
In reply to #5

Re: VCB Tripping

08/10/2014 11:27 PM

Hello Sir, OP said transformer is disconnected and still trips...So where is this Inrush current from ?

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#9
In reply to #8

Re: VCB Tripping

08/11/2014 12:06 AM

Please read the sentence carefully.The output from the transformer is disconnected.This means secondary side of the transformer is disconnected.The inrush current will prevail irrespective of load on the transformer.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#10
In reply to #9

Re: VCB Tripping

08/11/2014 1:36 AM

Yes,..You are correct. OP has to check the relay setting and take the tripping data from the Relay if possible. Normally Trasformer trips during the first energization and it will be Ok for second try. However, check the settings for the short time, long time and earth fault. Inrush current will creat a current unbalance and Relay will sense the unbalalnce current as earthfault. Hence it trips.It happends in some relays where there is no inrush current protection.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: VCB Tripping

08/09/2014 5:31 AM

The VCBs in the outgoings of RMUs come with self powered protection relays. It seems the relay is not set correctly.

It appears the protection is operating on transformer inrush and causing the trip.

What is the make of RMU and type and model of the relay!

__________________
Raghunath
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#7

Re: VCB Tripping

08/09/2014 7:25 AM

Fine, some have responded with remedies. But it is always better to mention makes of the machines and also the indications if any the system provides. Tripping of VCB could be due to many reasons and shortlisting of faults without all those details is a super expert's judgement I feel. feed a bit more for analysis... ALos provide your analysis if done with views or say could not analyse because....reasons.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (2); Fredski (1); M.R.Iyengar (1); raghun (1); ramvinod (2); SHOCKHISCAN (1); Simon Wan (1); TonyS (1)

Previous in Forum: Need A Bit Of Help Getting The 4th Axis On My CNC Working.   Next in Forum: Riser Conductors of Lightning Protection System in a High Rise Building

Advertisement