220 VAC Electric Baseboard Heater Without A Ground

12/21/2016 3:07 AM

I installed a 220VAC baseboard heater over the weekend and I didn't use a ground (I used the existing wires - well almost, but for argument sake, we'll say I used the existing wires). Here's the layout, 110VAC hot hooked up to heater. Other 110 VAC hot hooked up to thermostat. Other side of thermostat hooked up to other side of heater. When the thermostat closed the circuit, the heater would see 220VAC. When the thermostat opened the circuit, the heater would only see 110VAC on one line and the other is open.

My question is about safety. The heater manufacturer recommends the heater to be grounded. The Romex has a ground (2 conductor with ground), which I wired to the ground on the heater. The other end of the Romex (where it hooked up to the thermostat) has the same wires (2 conductor with ground), but the ground isn't hooked up, because the supply lines don't have a ground or neutral. I screwed the ground wire to the metal utility box, but that's not a ground (we don't use conduit).

Based on what I did, is this a safe way to install the heater? What bad things can happen (shock or fire)? There is a circuit breaker (double throw) on the breaker panel, but no Ground or Arc Fault Circuit Interrupter. Or, is it safer to wire it up without a ground?

One other piece of information that my be helpful. The condo is on the second floor, so there's no risk of the floor being a ground.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#184
In reply to #183
Find in discussion

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/30/2016 8:41 PM

Then the diagram is wrong: It has a fused neutral and an unfused live phase.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#197
In reply to #184

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 2:25 AM

Good catch.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#199
In reply to #184

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 4:26 AM

As I said, its whatever you want!! Try connecting blocks for example....I would have modified it if I had noticed that before....

I personally do not see them as fuses and although neutral fusing does take place in certain "backward" countries, its not anything that I would wish to see where I live.....because in most counties, neutral and ground are usually linked at some point!! e.g. a safety concern.

I simply took the diagram off the internet (little choice) to demonstrate how the US managed domestic supplies, in comparison to most other countries.

The US system when used properly and kept up to date is fine (my personal opinion not fact), especially if RCDs are used in each and every install (sadly far from true!).

But if used incorrectly or latest E.code simply ignored (the laws appear to need to be changed for older properties), appears to become possibly quite dangerous to users.

This blog being a perfect example of that!!

Many are simply blind to the bad possibilities of an out of date system, or incorrect connection, or even simply ignoring previous local E.Codes that still might have prevented certain accidents.....some people appear to need to lose a loved one, to make them change.....I am at a loss to understand their attitude in such matters....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#198
In reply to #182
Find in discussion

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 4:09 AM

Whatever you want them to be!

The only limit is your imagination!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#61

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 7:37 AM

"Question is about safety"!

I can think of an option to make your un-grounded installation safer..

By adding an Isolation transformer in-between the circuit breaker supplying the 220 volts and the (heater + thermostat) heating system..

A 1 KVA, (220 volts) 1:1 isolation transformer with grounded case can be placed next to the water heater. Connecting the ground wire to the transformer instead of the heater!

__________________
vsar
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#63
In reply to #61

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 7:54 AM

It's not a water heater.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#68
In reply to #63

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 8:29 AM

I dunno. Maybe the roof leaks.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#81
In reply to #61

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 10:35 AM

Sure sounds like a very expensive alternative to replacing a short section of 12 AWG Romex...

By the way... even when the transformer is not supplying any current to the heater, a 1 KVA isolation transformer will pull a good bit of energy just keeping the core magnetized, so there would be a on-going monthly charge for this approach as well.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#82
In reply to #81

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 11:35 AM

Not if the thermostat switched the transformer on an off!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#85
In reply to #82

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 11:50 AM

True... but...

The intensity of the magnetizing current inrush (the transformer winding being a dead short until the back emf increase the impedance of the winding) would destroy the thermostat in real short order.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#86
In reply to #85

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 12:01 PM

Probably, but there are devices to place across the contacts to handle that inrush, also, there are solid state relays that can handle that really well too.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#88
In reply to #81

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 12:25 PM

IF key issue is life safety due to electrical shock hazards, etc......

The 1 KVA isolation transformer suggested was really an overkill, and may be a bit expensive, in my opinion without a doubt it will make the OP project safe for everyone concerned..

__________________
vsar
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#90
In reply to #88

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 12:32 PM

Agreed...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#100
In reply to #88

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 1:57 PM

GA. Very true.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#186
In reply to #61

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/30/2016 11:55 PM

Great idea, but a couple problems:

1. Where would the isolation transformer be placed? This is a baseboard heater in the master bedroom.

2. Where would I get the ground for the isolation transformer? If there were a ground nearby, I would've ran it to the heater. There isn't a ground close by.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#201
In reply to #186

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 9:19 AM

The needed isolation transformer can be installed /wall mounted right next to the breaker box with its case grounded if or as needed.. With CB power Off, remove and transfer existing connections to the transformer. Run two new short wires from the breaker to power the isolation transformer...

Existing wiring for the baseboard heater can remain as-is, yet making it electrically safe..

__________________
vsar
Register to Reply
4
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#76

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 9:47 AM

Ok... here goes.

The following is true for most jurisdictions in North America.

With respect to buildings wired long ago; as long as nothing changes in the wiring of the structure, they are still considered as legally being a code compliant installation today.

However, as soon as you change anything with the wiring, what ever it is you are doing must be done under the requirements of the current code being enforced in the jurisdiction.

Note that the replacement of a faulty strip heater with a like rated model might be allowed to be done under the code that was enforced when the building was built, but it might not as well. Only your local AHJ, or a pro licensed in the jurisdiction, can answer this question.

Some jurisdictions allow anyone to do such replacements and others do not. For example, in my jurisdiction (I am the Chief Inspector of my jurisdiction) a home owner may do this work ONLY under a valid installation permit.

A "home owner permit" may only be issued to a home owner if the work is being carried out in a fully detached residential occupancy.

The idea being is... if you wish to risk your life and property, that is your right, but, you do not have the right to assume that risk on behalf of your condo neighbours.

So... as a Safety Regulator, my final advice to you is, you had better check what you are legally allowed or not to do in your particular jurisdiction and do only what is allowed.

Doing otherwise can and does expose you to all sorts of potential legal issues.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#79
In reply to #76

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 9:54 AM

GA

It is similar in the UK, with Part P of the Building Regulations being applicable, and guidance on best practice given by the aforementioned BS7671. Documentation indicating compliance with the above is a formidable shield in law and will maintain popularity with the building's fire insurer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#113

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 6:44 PM

As there are no obvious grounds nearby, possibly a double pole GFI circuit breaker would be in order. This won't prevent the case from going live, but if a short to ground occurred, either through personal, pet or some other type of path to ground, the breaker would trip before death or fire could occur.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 273
Good Answers: 12
#114

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 11:07 PM

I'm working on a 120 V heating system for a greenhouse. The problem I encountered is the thermostat was not rated for 120 V for heat. It IS rated for 120 V to control a cooling fan. The current rating isn't adequate to operate the heater (about 10 amps). I'm re-wiring it to include a 24 V transformer and a contactor.

I looked at the Cadet baseboard heater's website and see that they offer thermostats. My question is if that thermostat can handle the required amperage, or if it requires a contactor, too.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#115
In reply to #114

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/22/2016 11:46 PM

They probably have some models that will handle the current and voltage. Look at their website.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#190
In reply to #114

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 12:42 AM

I didn't use the Cadet thermostat, but looking at the specs, I'd say there is no problem using it without a contactor.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#122

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/23/2016 9:30 AM

Dibs on the first 'shiney'

Register to Reply
2
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#134

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/23/2016 8:31 PM

The surprising array of responses from people i consider to be experts has perplexed me. I have done some digging and found that the terms bonding, earthing and grounding are not interchangeable. http://www.eece.uwa.edu.au/students/safety/elec3307/earthing-cpd ...The simple fact that different countries afford personal protection by using different methods/systems appears to have caused the different responses. Some countries use the equipotential bonding method and others use a single earth rod driven into the ground. To further mix things up this rod can have both the earth and the neutral conductors joined to it in one country but not in another. ....When i re read the posts i can practically tell which country the respondent is from. It was a slide presentation from an Indian University that addressed the differing systems. I guess the last 100yrs of Indian history has led to a mix of systems in their country. http://www.slideshare.net/AZMAT0/electrical-safety-and-risk-assessments Look at slide 21. .....The IEC has identified, and spelled out, several different types but they seem to use different nomenclature. (Different to that in the Indian slide show.) ......I know that in Oz a single earth rod is preferred but multiple earth rods are allowed under very strict provisions. I don't own an A.S. 3000 wiring rules ($1000's) so i can't immediately find the relevant reference.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#193
In reply to #134

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/31/2016 1:08 AM

Thank you. This is very pertinent information and helps me understand the vast differences in opinions here.

I should've included in my post that the condo is in the Western US.

GA to you!

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Power-User

Join Date: Jun 2013
Posts: 145
Good Answers: 5
#142

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/26/2016 10:38 PM

Since you get 110v on one side when the thermostat breaks and 220v when it makes, it sounds like your heater is "single phasing" 220 with 2 phases and your hot leg upon breaking is using the ground wire as your neutral.

If so, I believe your hookup is illegal and unsafe without a 4th conductor to act as a dedicated wire for fault currents.

I recommend looking up some you tube videos on the difference between neutral and ground to get a better picture. After looking up this topic, you may understand the importance of bonding.

Register to Reply Score 2 for Off Topic
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#145
In reply to #142

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/27/2016 5:28 AM

I have negated the OT someone gave you, as you are correct with regard to safety.

One could say, the single most important part of this whole blog!!!

You wrote:-

If so, I believe your hookup is illegal and unsafe without a 4th conductor to act as a dedicated wire for fault currents.

Might have been clearer if you had written:-

If so, I believe your hookup is illegal and unsafe without a 4th conductor to act as a dedicated wire for earth fault currents.

Though you were correct enough for me personally I would like to add....but not for some others here apparently.

Have a great day.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2013
Posts: 145
Good Answers: 5
#156
In reply to #145

Re: 220 VAC Electric Baseboard Heater Without A Ground

12/28/2016 8:15 AM

Thanks for sharing the feedback! I do appreciate the details.

Register to Reply
3
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#214

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/02/2017 3:29 PM

Since I work as a designer of radiant electrically heated floors, the equipment I work with uses a thermostat which switches both lines of the electrical connection on and aff and uses a ground fault interrupt on both lines to boot.

You did connect a ground from the non-thermostat line, which provides some protection. However, going to a gfci breaker on the circuit would likely be a good peace-of-mind move as well. I've run into situations where the insulation material in the heater elements can go slightly conductive over time at elevated temperatures and the gfci adds a layer of safety concerning shock hazard. My only other concern is that the single leg thermostat leaves one leg hot at 110V in the unit even with the thermostat switched off, which is less than ideal.

Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#215
In reply to #214

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 5:50 AM

GA

But:-

"Understatement of the Year 2017?"

My only other concern is that the single leg thermostat leaves one leg hot at 110V in the unit even with the thermostat switched off, which is less than ideal.

That is one of the major drawbacks of the US 110VAC system, when using it for a 220VAC device.......not disconnecting both legs in the event of a malfunction, or even a thermostat switching, because the dummies only buy one that is single pole!!

I really don't know just how often I have mentioned RCDs that remove BOTH legs at the same time, on this blog!! First time Post #53 I believe. I cannot be bothered to count back,but many, many times.....

Its also appalling just how many here offered (poor quality) advice, most not even once mentioning RCDs/GFCIs and the like!!!

Not forgetting the OP who not only does not (want to) understand how an RCD/GFCI functions.....but argues about it needing a ground connection!!!! Which he believes that he does not have at all in Condo!

Let alone the room with the heater installed.

http://en.wikipedia.org/wiki/Residual-current_device

I wonder if he will ever come back and let us know if it shocks or even kills someone, (maybe because it will be himself?) assuming no extra safety devices or ground as he wants to(has) install(ed) it?

From that link I posted:-

A residual-current device (RCD), or residual-current circuit breaker (RCCB), is a device that instantly breaks an electric circuit to prevent serious harm from an ongoing electric shock. Injury may still occur in some cases, for example if a human falls after receiving a shock. In the United States and Canada, the device is more commonly known as a ground fault circuit interrupter (GFCI), ground fault interrupter (GFI) or an appliance leakage current interrupter (ALCI).

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#216
In reply to #215

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 1:42 PM

I just looked at a 110vac installation on a single line thermostat that used the old style mercury bulb switch on a bimetal spiral coil and no GFCI. Lots and lots of these around and most people don't want to get involved in disposing of the mercury.

It must be said, though, that it takes more effort and determination to kill yourself with 110 than it does with 220, or at least a more highly refined level of stupidity.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#217
In reply to #216

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 3:08 PM

There are arguments for and against each voltage, but I find this link to be as good as any, it maintains that "complacency" kills.....at 110VAC!!

Which-one-has-more-fatality-110-volts-or-220

You have forgotten that, although voltage may burn, it's current that kills!!! Also, it's a relatively tiny amount of current!!

Here:

Electric_shock

You can read this that demonstrates that 110VAC kills more people "per capita" than 220VAC does:

There were 550 reported electrocutions in the US in 1993, 2.1 deaths per million inhabitants.

In Sweden, Denmark, Finland and Norway the number of electric deaths per million inhabitants was 0.6, 0.3, 0.3 and 0.2, respectively, in years 2007-2011.

I was surprised, as I expected 110VAC to be less dangerous (PROVIDED IT WAS INSTALLED CORRECTLY)!!!! But apparently, it's not!!

Sorry that the figures I found were not world-wide complete.

I found this discussion to be very illuminating (pun intended!):

Differences between the UK & USA Electrical systems

Which demonstrates that the UK system, as a whole, is far more orientated to safety than the US systems are.

I found the whole discussion online to be very informative.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#219
In reply to #217

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 3:50 PM

Sorry, you cannot make any comparisons about which voltage is more lethal because stupidity plays a big role in the stats. All you can say is "...at 110VAC and above..." A 12VDC car battery can kill you if the circumstances are just right.

The "let go" threshold is about 10mA; 30mA can cause tissue damage, fibrillation, and/or cardiac arrest (depending upon the path through the body, its weight, and condition). 10υA (microshock) can kill if the electrodes are inserted under the skin and the pathway passes through the heart. DC through skin contact requires 300-500mA to cause fibrillation.

Voltage is deliberately left out of the discussion because perspiration, area/point of contact, age, physical/skin condition, etc. all affect the impedance the body presents to the source and, therefore, its reaction to the stimulus.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#226
In reply to #219

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/04/2017 12:13 PM

I was not making wrong comparisons as you imply with your post. Why didn't you mention the safety factor helped by a correctly installed RCD for example......

In fact, you should have answered Post #216 as I was, not simply jumped in the middle...

As you are going off at a tangent with regard to that post that I had answered, a post that maintained (wrongly) that 220VAC kills more often than 110VAC, which is simply wishful thinking!!!

Only theoretically does it kill more, (under identical conditions maybe) but not in practice, as my first link maintained, complacency is the biggest problem with 110VAC, and I also maintain that poor design, poor electrical codes, poor laws not enforcing the newest codes and and and and......are the basic causes....

I know how electricity kills, also I know how to make it safer by installing it correctly.......

Also how it should be installed to give the user the best chance not to get a shock!

I also know that its the current that kills, not the voltage, many here obviously don't, if throwing around comments that accuse a (higher) voltage of killing more people!!!

It appears that you only read part of my post!!! Try reading it and the links it contains fully, it was Post #217!

The Poster of #216 obviously does not have a clue.....as many people don't have a clue, who have not had the necessary training......so you cannot blame him really.....

I also have met (sadly, far too) many electricians who do not have a clue what they are REALLY doing and why. They learned a method, but not why and how......even on this blog there is at least one that stands out in that way!!! He is NOT alone!! Sadly!!!

Even some UK electricians simply cannot understand just how good the code is British Standard BS 7671!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#232
In reply to #219

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/05/2017 6:22 AM

I stumbled on this, demonstrating again that its not voltage that kills, its the current and the horrendous burns that often result can kill, eventually:-

The attempt to take the “ultimate” selfie turned into a tragedy as the she accidentally touched a live wire on top of a train. 27,000 volts passing through your body are not exactly a pleasant experience to go through or even watch.

The girl did not die because of the initial shock, but because of the burns that covered an important percentage of her body.

We can only wonder why on earth a beautiful girl like her needs extra attention in social media. She probably had thousands of friends and each photo of her scored at least 100 likes. We will never answer this.

Here is a picture of the teenager, before the accident:-

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 3)
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#220
In reply to #217

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 5:50 PM

Thought that would get a response.

I'm noticing a lot of "double insulated" appliances with no ground protection and a lot higher level of use of GFCI.

I was also surprised by the latest wave of 53V lithium ion battery powered landscaping tools. You can actually get quite a jolt from them under the right circumstances.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#223
In reply to #220

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/03/2017 10:05 PM

Double insulated appliances/tools have no direct path from the energized parts to any openings or exposed conductive parts of the device, hence no ground pin or polarized plug is required.

Increased use of GFCIs and AFCIs is a result of continuous changes (aka Code Creep) in the NEC and/or local codes, which keep requiring these devices in more and more locations.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#225
In reply to #223

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/04/2017 11:22 AM

I was looking at the published stats and there is a really good correlation between number of installed GFCIs and reduced number of deaths by electrocution.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#227
In reply to #225

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/04/2017 12:16 PM

Have you a link for us all?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#231
In reply to #227

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/04/2017 7:54 PM

How's this, one of many...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#233
In reply to #231

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/05/2017 6:40 AM

GA

To my mind, for this particular blog, that was the perfect post!! which gets a GA of course....

With any luck, a few others here will be of the same opinion!!!.

It was sad that I had to ask for it though!!

But really great that you posted it!!! Many thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#242
In reply to #231

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 4:09 AM

Good chart! There are still many homes that don't have gfci's in the bathroom/kitchen. When I bought my properties, most didn't have them in the bathroom or kitchen. In one house, there was one installed in each bathroom, but it was installed wrong.

I think pre-gfci in the US, a large percentage of electrocutions come from dropping electrical devices in kitchen sinks and bathroom tubs/sinks. Common sense tells us that gfci's will reduce the number of electrocutions, but your chart gives us the actual data.

GA to you!

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#240
In reply to #215

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 3:36 AM

If you've never been in a pre mid 60's era home in the US, how can you comment on where a ground exists? Do you even know? And if so, please tell me where the ground is in the bedroom in question. I'm speaking of the ground that will magically appear when the heater decides to have an electrical fault. And where has this mysterious ground been over the last 50 years in the hundreds (maybe even a thousand) of condos in the complex. Why hasn't the associate upgraded the so called "dangerous" heater. Yes, my home owners association does upgrades to our units - it's built into our association dues. You would think their multi million dollar liability policy would cost them a fortune if things were as dangerous as you claim them to be. Either that, or the insurance company is just plain stupid, which I don't think is the case.

Using practical business sense, one could assume that there are nearly zero (I can't say there are zero, because I don't know) claims of people getting electrocuted by their ungrounded heater systems, which is the liability of the association. If there were a lot of claims, the insurance premium would be very high and our association dues would've gone up considerably, right? Or is the entire system defective?

You tell me.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#244
In reply to #240

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 6:46 AM

You posted:-

You tell me.

I have done, several times, So have several other people here, time after time, but apparently you don't understand electrics.

Will telling you again help you to understand? How many more times must you be told?

You tell me!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#247
In reply to #244

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 5:52 AM

Wow, you just don't get it, do you?

I'll spell it out in a little clearer way.

1. These heaters have been in about 10,000 condos in my area for 50+ years.

2. Our association insures these homes.

3. The insurance company charges a set rate based on risk factors.

4. The risk factors are based on things like safety and historical data such as the number of claims.

5. Our association dues have not gone up considerably, nor has our Board of Directors sent us notice that we would have an increase due to the cost of insurance.

6. Insurance companies have some of the brightest minds working for them - they're the ones who come up with complex algorithms to determine premium cost. If you look at the profitability of insurance companies, you'll see they make a lot of money, hence it can be concluded that the people who determine premiums truly know what they're doing.

7. The logical conclusion is that these heaters must not pose a big risk, because if they did, there would be numerous claims and our insurance premiums would've gone up.

8. Or use the null hypothesis. Because of our heaters not being grounded, they are dangerous; many people are electrocuted and their homes catch fire.

9. To disprove #8 is easy. If #8 is true, then our insurance premium would be high.

10. If there were a reasonable risk, say 0.25% failure rate per year per heater, then we'd have over 100 insurance claims.

11. But we didn't have 100 claims, so drop it to 0.025% failure rate per year per heater and we'd have 10 insurance claims.

12. But we didn't have 10 claims, so drop it to 0.0025% failure rate per year per heater and we'd have 1 insurance claim.

13. But in the 50 years the condos have been there, I know we haven't had 50 claims. My guess would be 10, if even that many. So on the high side, 0.0005%.

You claim that I don't understand electrics. Well, I guess those dangerous heaters don't also, because over 50 years of service, they've proven you wrong.

And by the way, you never did tell me why I can hold a hot in one hand and not get shocked - you know, there are all these magical grounds all over the place, so shouldn't I get shocked? What am I missing? Or are you wrong?

__________________
Enjoy and be happy! Life is too short!
Register to Reply Score 2 for Off Topic
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#251
In reply to #247

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 11:52 AM

You said:-

Wow, you just don't get it, do you?

I would have thought that only one person here "didn't get it" and we (except him!) all got "it", days ago!!

Also, many thought my blonde joke very fitting too!!! But do remember:-

Sayōnara = Japanese for Goodbye!

Not to be confused with Cyanide, which is Goodbye in any language......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#256
In reply to #251

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/24/2017 3:08 AM

Your response to my last post lets me know that you don't have a response to business and risk. My only recommendation is to stop exaggerating things to try to prove your point. You are not smarter or have better data than insurance companies and if you think you do, then why don't you open your own insurance company and prove them wrong?

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#258
In reply to #256

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/24/2017 4:17 AM

You prove, yet again, with your post(s) to be even mote stubborn and ill informed than anyone here ever dreamed or thought you might be.

YOU HAVE TO BE RIGHT, NO MATTER HOW LIMITED YOUR KNOWLEDGE IS, NO MATTER HOW MANY PEOPLE HERE POST, DETAILING THE REAL REASONS WHY ITS DANGEROUS, YOU HAVE TO BE RIGHT!

The people here are generally intelligent, with good knowledge, understanding and background on this and many other subjects.....it beats me why you came here at all!!!

On a personal level, sadly you come over as a possibly previously spoilt child, maybe an only child, maybe the "Baby" of the family, possibly.....

You also apparently fit the profile of a sociopath, online at least.......possibly not in real life.

Stay well, stay fit and I hope you manage to grow up before something serious happens!!! But that might be the only possible way for you to finally learn something useful!!!

I hope for you and your family, that this stubborn "streak" ONLY extends onto the IoT and not out into your "real" life.....that would be dreadful for them!!!

I'm off now, no point in flogging a dead horse!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Apr 2015
Location: NYC until mid 2015, currently NC
Posts: 756
Good Answers: 8
#254
In reply to #247

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 9:44 PM

Re your #6:

Insurance companies do not pay claims resulting from negligence.

All one of the lawyers representing the insurer has to do is present a copy of the instructions provided by the seller for PROPER installation of the product.

__________________
Good judgment comes from experience, and a lotta that comes from bad judgment.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#255
In reply to #254

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/13/2017 5:03 AM

GA

Fully correct.

To put it bluntly, in a worse case scenario:-

No payout with regard to any damage done to the building concerned, possible damage done to other nearby buildings, parked cars, people injured, people killed or the costs of the fire department and police!!!

Did I miss something?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#245
In reply to #240

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 11:44 AM

Everywhere in your home is ground, whether it is enough to kill you on a given day is a crap shoot. A little moisture, a few trace minerals, even capacitive coupling of your ac house wiring is enough to make any perceived insulator a conductor. Just touching the live side of any circuit, either side of your heater, is all it takes.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#246
In reply to #245

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 1:45 PM

GA

Well put, but I believe he will not understand you, or he is simply not "holding" enough brain cells to understand....One or the other.....

Either you, someone else and/or I have said this several times....already, I forget which....but its hardly important as he does not believe anyone at all, anyway!!!

Its a bit like the awful sexist blonde joke:-

Q."When has a Blonde a full set of brain cells, in good working order?"

A."When pregnant!"

Sadly, he cannot get pregnant!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#239
In reply to #214

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 3:27 AM

I appreciate your input. As someone who designs electric heating products, you have experience in the field.

You are correct that one of the 110V legs runs straight to the heater and a fault in the heater could make the entire unit hot. I thought about running a double pole thermostat, but I chose not to. Maybe a bad move - I'm not sure.

When you install the heated floors, where do you install the gfci? At the circuit breaker or do you install a gfci outlet ahead of the heater thermostat?

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#243

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/11/2017 4:22 AM

I want to thank everyone for their advice. Some is very theoretical, which may not be applicable to me, but it's nice to see how people here think. Some answers cited code and what should be done based on the code. Good information. Still other advice was based on a potential risk, something I wanted to know, but unfortunately, much didn't make sense, since there was some incorrect assumptions made. Still others felt the need to chastise me for doing something that they felt was unsafe, however I never understood the practical side of doing a fairly major modification when the risk is extremely low. I did try to explain that there have been very few, if any failures in 50+ years of these ungrounded heaters installed in the large number of condos in our complex. My condo has three of these heaters and not one has failed in 50 + years. I don't want to hear fear mongering; I want to hear good advice and facts.

I do want to thank everyone for their advice and if there is anything else you can add to help the situation, please do so.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#250

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 9:31 AM

Since this thread seems to go on forever, I'd like to add one final batch of data on condominium burned.

358,000 results in 0.32 seconds. There are certainly multiple entries for each incident, still that says something.

Just because everyone else does it does not make it safe. Just because you have yet to electrocute somebody, does not make it safe.

Just to be thorough I will finish with condominium heater electrocution.

490,000 results in 0.52 seconds. There must be a traffic jam on the internet somewhere.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#252
In reply to #250

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 11:55 AM

GA

You make a very valid point for ANY normal person..........

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#253
In reply to #250

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/12/2017 12:28 PM

I looked around a bit using similar search arguments to yours and I found a problem with them that I do believe nobody here has taken into account and did not result because of a bad or missing ground, but killed anyway:-

Baseboard-heater-blamed-for-fatal-Md-fire

Smoke alarms might have prevented the tragedies.....

Here also:-

http://www.summitdaily.com/news/baseboard-heaters-cause-recent-fire/

Back to electrocution:-

Milwaukee-infant-electrocuted-after-sleeping-in-bed-with-mom-another-child-due to Baseboard heater

Here is interesting, and I believe applicable to this blog:-

5-reasons-to-replace-your-wall-outlets/

Go down to the paragraph labelled:-

Stuck with 1980s Technology?
(that's like the Middle Ages in today-speak)

Also:-

Woman Killed in old Condo with no proper ground wiring

Here is some good and sensible information with regard to Thermostats, where it states clearly that two pole are needed for 220-240VAC installs of heaters:-

http://www.king-electric.com/pdfs/TSTAT_ES_instructions.pdf

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#257
In reply to #253

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/24/2017 3:12 AM

Oh my goodness! I quit! If it makes you feel better; You win. I'm done.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Participant

Join Date: Aug 2020
Posts: 4
#259

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/07/2021 4:07 AM

Many thanks to Andy Germany for the information, I had similar problems as the author of the post and you helped me solve them. Safety is very important to me because I have small children and I would not want them to be electrocuted or start a fire.

Register to Reply Off Topic (Score 5)
Participant

Join Date: Aug 2020
Posts: 4
#260
In reply to #259

Re: 220 VAC Electric Baseboard Heater Without A Ground

01/08/2021 9:10 PM

Usually here https://buyersimpact.co.uk/ I look at reviews of similar equipment. And I chose a high-quality electric baseboard heater, but I was able to deal with the installation only thanks to this thread. Next time I will immediately turn to the professionals.

Register to Reply Off Topic (Score 5)
Register to Reply Page 3 of 3: « First < Prev 1 2 3 Last »

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andrew Westman (28); Andy Germany (53); Autobroker (51); Brave Sir Robin (3); Casper71 (2); English Rose (1); garyrich2000 (2); GordonCornish546kW (2); Ivanov327950 (1); JIMRAT (6); JohnDG (11); Jpfalt (4); JWthetech (1); lyn (6); North of 60 (21); PWSlack (4); RAMConsult (10); redfred (9); rwilliams (12); setlock77 (1); SolarEagle (5); steve45 (1); tcmtech (1); tonyhemet (4); TonyS (2); Tornado (9); vsar (7); wayneelowe (1); WJMFIRE (2)

Previous in Forum: Deaeration of Seawater For Process   Next in Forum: What Are These? (I Really Have No Clue)

Advertisement